In which case, do they have a leg to stand on in terms of forcing us to use their own sub-contractors and charging a ridiculous amount for the 'privilege'?

And when you say "that person who certifies it", are you referring to issuing a Part P cert or something along the lines of an EICR?

There is no such thing as a "part P cert". When we carry out notifiable work, we log it with our scheme provider, and the scheme provider notifies LBC and sends the homeowner a certificate. The electrician does not issue any kind of certificate himself, just test results.
 
Building control have to foot the bill not the section 1.26 of part P says this. but for some reason when you download this its blank just in that section ? look on line at this link
http://www.planningportal.gov.uk/uploads/br/BR_PDF_ADP_2006.pdf

page 11
bottom right
Hmmm, 1.26 of Part P which includes the 2010 amendment (http://www.planningportal.gov.uk/uploads/br/AD_P_wm.pdf) states otherwise:

"The building control body may choose to carry out the inspection and testing itself, or to contract out some or all of the work to a specialist body to carry out the work on its behalf. Where the building control body is a local authority it cannot require the building owner to undertake this work. However, under the Building (Local Authority Charges) Regulations 2010, the authority may charge a higher building control charge when first notified the work or levy a supplementary charge later, based on the recovery of its costs."
 
Last edited by a moderator:
Having spoken to Building Control, they will only accept having the work 'tested' by their own sub-contractor and want a fee of £380 for this 'regularisation' work. We queried whether our newly found electrician can undertake the same 'tests' that their sub-contractor would and obviously at a much more sensible price. Their response was a firm 'no'.

Do we have any options available to us other than pay Building Control this extortionate fee? Surely they can't get away with charging such disproportionate amounts for work that any other competent person could do at the correct market price?

The term 'regularisation' work is used by many LABCs for notifying the work after it has been carried out.
Under Part P there are three methods for notification.
One is to pre-notify the work and pay the appropriate fee, the LABC will usually inspect the work once or maybe twice, and as long as the work is satisfactory, issue a Building Regulations Compliance Certificate.
In many cases the LABC will waive the inspections if they are happy that the tradesman is suitably qualified, and that the tradesman will issue an EIC/MEWIC upon completion.
The preferred method is to employ a tradesman who is registered with a Self Certification or Competent Persons scheme. The tradesman will then issue the Building Regulations Compliance Certificate.
The third and most expensive method is to notify retrospectively. The LABC will usually arrange for an Inspector to conduct an inspection and issue an EICR. The LABC then if the report is acceptable issue the Building Regulations Compliance Certificate.

Although the additions listed are not notifiable under Part P, it appears that either a planning application was made, or some form of notification was made to the LABC for the whole extension.
If the wiring additions were included in either a planning application, or LABC notification, then the LABC would apply the same criteria as if the work was notifiable under Part P.
As such if inspections have been waived and an EIC/MEWIC is expected and you are unable to produce one, the LABC will treat this as a retrospective notification, and will charge the fee accordingly.
It is not just the EICR that you wil be paying the LABC for, but also for regularising the retrospective notification.

You could argue extenuating circumstances, and that the electrical work is not notifiable under Part P, but you are still left with work that does not have an EIC/MEWIC and as such does not comply with the Electrical Regulations.
You will have to convince the LABC that the work is not notifiable, and without an EIC/MEWIC, that is going to be very hard to do.
Do the initial plans indicate that the existing circuits are to be extended rather than new circuits installed?
 
You could argue extenuating circumstances, and that the electrical work is not notifiable under Part P, but you are still left with work that does not have an EIC/MEWIC and as such does not comply with the Electrical Regulations.
You will have to convince the LABC that the work is not notifiable, and without an EIC/MEWIC, that is going to be very hard to do.
Do the initial plans indicate that the existing circuits are to be extended rather than new circuits installed?
What is the difference between an EIC/MEWIC and an EICR? It is my understanding that anyone can issue an EICR for work after it has been completed by someone else.

The conversion did not require any plans and thus there was not mention of any electrical work. I would imagine it should be obvious that any garage conversion will require at least some electrical work anyway.
 
Hi,

Why don't you start a complaint procedure with the NICEIC regarding the sparky that you used stating that no certification has been provided and you doubt the integrity of the work that has been carried out because you can't get a certificate from him for the work he has done?

It is my understanding that if we as NICEIC registered electricians do not comply with regulations (to which certification is included) then the NICEIC will get involved and help rectify the situation, as they at the NICEIC are there to protect the consumer first and foremost.

I will have to check to be 100% sure but I think that it is in the NICEIC's small print that if you (the customer) are not happy with work carried out by a registered electrician and the NICEIC agree then they will insist the electrician in question has to rectify any regulation irregularities at his own expense, and if the electrician will not comply then the NICEIC will instruct another approved electrician to rectify the shortcomings also at the original electricians expense 'or they may be striken off i think'.

Hope this helps.

Regards Nige.

PS The work as explained was not notifiable to LBC and only a minor works cert is required because there was no work in a special location nor any new circuits added
 
What a complicated catch 22 fiasco is this part p claptrap

Get yourself a registered spark.move the sockets a couple of inches,ditto the lighting alteration,have a minor works certificate and hand it over
 
this spark could argue the work is not finnished and he does not intend to finish because x,y,z and therefore i would expect it is hard to pin him down, also he may have won the lottery and not give a stuff
 
Thanks Nige. The NICEIC did summarise their complaint procedure to us this afternoon. Basically we need to write a letter to the spark, wait 7 days, then if we do not hear from him, formerly complain to them (the NICEIC), and they will then attempt at finding a solution. However, that currently seems more long winded than figuring out whether LABC need a cert in the first place, and if so, whether they can charge so much.
 
TMess,

The way I see it is that LBC want a certificate to cover work done in the worked on areas not a Part P certificate. If you got another sparky to adjust and test all of the newly installed electrical outlets and issue a minor works certificate this would suffice.

To answer an earlier question you asked a Minor Works Cert covers basically alterations and additions to existing circuits, an Electrical Installation Cert covers newly installed completely new circuits and an EICR is carried out on an installation to test its integrity and is for information about an installation and its state of repair which may result in either a satisfactory or unsatisfactory result.

Regards Nige.
 
TMess,

The way I see it is that LBC want a certificate to cover work done in the worked on areas not a Part P certificate. If you got another sparky to adjust and test all of the newly installed electrical outlets and issue a minor works certificate this would suffice.

To answer an earlier question you asked a Minor Works Cert covers basically alterations and additions to existing circuits, an Electrical Installation Cert covers newly installed completely new circuits and an EICR is carried out on an installation to test its integrity and is for information about an installation and its state of repair which may result in either a satisfactory or unsatisfactory result.

Regards Nige.
Does a Minor Works Cert (MEWIC?) or an EIC get registered with the NICEIC who would then forward the registration to the LABC? Or is it merely a certificate with test results that gets written out by the installer and handed over? The LABC have stated a number of times that they check for work certificates 'online'.
 
View attachment 14568could this be the section i was trying to show you TMess but when i looked back at it for some reason it changed, but i had a photo of it.
Have a look at my reply with the updated Part P document on the previous page of this thread. You linked to the older Part P (before the 2010 amendments) which has different wording within paragraph 1.26 than the newer edition.
 
Most Part P certificates are filed on-line but as for all other certification it comes direct from the installer and you don't have to be registered with bodies such as NICEIC to provide it, you can simply use photocopies of certificate examples from BS7671 aslong as you have a code and number system.

The certificate should be issued directly to the person who ordered the work to be done from the electricians carrying out te work.
 
The other thing is dont worry as the job is not complete yet so no certs need to go to LBC, why say you, well the job is not complete due to the fact the sparks has not yet issued you with the certificate, or the body to whom he is registerd with. and he has not said he is holding the cert back for any reasons has he. tell building control to go and do one.
 
A bit of a work around the situation (some may say it's abit dodgey) but it may be possible to do as follows:

IF building control/LABC have no record at all of who did the original install (the guy who's done a runner) then if your new sparks is willing to test/inspect/sign off the install issueing a minor works certificate which you can then send a copy to LABC then alls good and LABC will be none the wiser.

Technicaly it's not the right thing to do as the installer should be the only one issueing the cert for the work (so i'm not in anyway suggesting this should become common practice) but circumstances have you abit screwed. Aslong as LABC dont know who the original sparks is then as far as they're concerned the new sparks IS the original sparks.If the new sparks is Part P and can certificate online then even better.

It's not right,it's not clever....but it is a work around the situation so you can get the job signed off by LABC (as i gather this is the main problem).....would however be interesting to know what actualy happens (if anything) with NIC*spits*EIC and if they do actualy chase the scarlet pumpernickel of a sparks done and give him a slapped wrist.
 

Reply to No Certificate For New Electrics And Local Authority Demands in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, I am a home owner and our builder has completed a garage conversion with the electrician installing a new 4 way distribution board. The...
Replies
18
Views
1K
Hi everyone. I'm the landlady of Railway Inn in Winchester, a grassroots music venue. I requested to join to increase my understanding of what...
Replies
18
Views
622
Evening all, Due to growth within the business we are looking for additional electricians to come on board to service upcoming contracts...
Replies
0
Views
278
Hello, in preparation for renting out our home we have requested an Electrical Certificate and our electrician is doing a few minor tidy up jobs...
Replies
6
Views
872
As per Part P of Building Regs, once electrical work is performed by a registered competent person, the installation certificate needs to be given...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock