doing a eicr today and the apartment im at, along with all the others, has no main fuse. there is a big service head, possibly containing individual phase fuses, but I've not opened it up.
from there you have single 25mm tails going in to each meter for each apartment, then in to an isolator switch, then swa feeding the cu in the apartment.

am I missing something?

cheers adie
 
That big service head is likely to be a multi service cutout containing 10 or more individual fuses.

Of course you haven't opened it, you're not allowed to open service heads or any other DNO equipment and you shouldn't have any need to do so.

The problem you have is not what is in the DNO equipment, but the fact that you don't have any protection on the consumers side of the meter for the distribution circuit.
 
no pics I'm afraid, could always get one tomorrow.
dave ,if this is the case then happy days, it would be nice to see what is protecting the 20M run of swa though.

It's not happy days because there is no fuse for the distribution circuit.
[automerge]1594244360[/automerge]
Does the large cutout look anything like this or a similar variation?


There are a few different designs out there and they are/were used for small blocks of flats.
 
I can see I've worded my reply poorly. happy days that there is probably a main fuse at least, but still cant see anything for the swa circuit.
[automerge]1594244857[/automerge]
yup, couldn't see it head on but I'd say very similar
 

Reply to no main fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, With regards to modelling a multi service distribution board, how would you guys model it in Amtech? I have tried using a TPN...
Replies
28
Views
4K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
786
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock