Non combustible switchgear

Discuss Non combustible switchgear in the UK Electrical Forum area at ElectriciansForums.net

WallaceP

-
Arms
Reaction score
235
hey guys, I had a quick search but couldn’t find any posts about this.
I recently done an inspection on a domestic property and found the electrical meter was outside in a service cabinet and the fuseboard was inside more than 5m away. I recommended installed a fused disconnector at the meter to comply with regulations and also for convenience if the fuseboard had to be isolated.
I would say this should be non combustible but I still see a lot of the plastic styles of these switches available. Such as LEMSF100.
Is it possible for this to be installed as it is outside the home? I think I would rather install a metal one anyway but curious to hear your opinion on the matter
 
No they’re not exclusive, anything can comply with more than one Standard.
However, in order to comply with BS7671, the Switchfuse must comply with the Standard which relates to Switchfuses, not the one which relates to Consumer Units.
 
That was pretty tame. In a domestic setting, in a scenario where a A3 CU is installed, doesn’t make sense to me that if a switch fuse was installed next to it, that could have a plastic enclosure, and comply.

Suppose any guidance, might be again that the designer would have to carry out that risk assessment or judgement.
 

Reply to Non combustible switchgear in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock