you still have to buy a seperate fire hood to use them!

why? is the floor above a separate dwelling?
 
Always a frequently debated subject here, and yes a normal domestic dwelling is treated as a single fire compartment, but there are other aspects to consider.

Plasterboard ceilings are also used to protect loadbearing and non loadbearing walls and floors from premature collapse during a fire, not just to make them look nice. Cutting gert great big holes in said plasterboard isn't going to help that.

Electrical Safety First Best Practise guide 5 issue 2 gives some guidance on this subject;
Best Practice Guides - https://www.electricalsafetyfirst.org.uk/electrical-professionals/best-practice-guides/

Down lights and flush CU's are mentioned, amongst other electrical accessories. Course no one mentions the holes chopped in for bathrooms for extractor fans (although this guide does)! And if your in a scheme, some of them advice the fitting only of fire rated downlights or fitting of fire hoods as standard.
 
Why do people still make none fire rated down-lights?
Got to do a quote for a new build where the client wants fittings that are not fire rated. Still waiting for quote from my wholesalers- but doubt they are cheap!

Round Trimless Magnetic Downlight - http://www.orlight.com/en/cat/downlights/ORL1018-1.html

why do these 'premium' fittings get made- but you still have to buy a seperate fire hood to use them!
With Orlight they are a direct to contractor supplier.

Maybe your wholesaler will have more luck than I have ever had with them, but usually the process is:

  1. Call them up to obtain the quote.
  2. Get told they won't deal with you over the phone and to email them instead.
  3. Send them the email stating the project quotation you are after.
  4. Wait a day or two to get a response along the lines of "to provide you with this quotation we need, The Architects Details, The Contractors, The Project Name, The End Users Details.
  5. Call the contractor back for this info (to which they never know the answers).
  6. Email Orlight back over these details.
  7. Wait a few days for a response saying "to enhance profit on this project this is listed as a direct to consumer project. Please advise your customer."
So yeah, cut out your wholesaler in this instance. The chances of them getting anywhere is pretty low (although saying that sometimes there are projects that can be placed through wholesalers. These are very rare though).
 

Reply to none fire rated recessed lighting! in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
We're doing a refurb of a takeaway restaurant. Client has asked us to re-use existing downlights and provided some additional ones of the same...
Replies
21
Views
3K
Evening Just want to clarify what is adequate for providing fire rating for lighting. My understanding is that if in an apartment block but has...
Replies
0
Views
693
So I am choosing my downlights and I was looking at the cylinder shaped fire rated downlights. The electrician mentioned look at LED slim recessed...
Replies
12
Views
2K
I posted last week regarding a lighting cable being too short in the wall to reach my new light fittings.this is still annoying me lol, I will try...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock