I'm writing an EICR in a department store in London

one of the section boards has a sub-main made up with 4 x single core 95mm MICC cables.
I have snagged that the gland plate is steel and there are no slots in place to counter the eddy currents.
(the loading is only 15 amps per phase when testing at about midnight)

But inside the section board the MICC's connect into a large set Din rail terminals to 35mm singles into the 100 amp MCCB.

I seem to remember that there is a reg basically stating where ever a conductor changes size there needs to be additional overcurrent protection

any ideas anyone?
 
The reg allows protection to be placed after the point in reduction of CSA if the cable is protected from mechanical damage and less than 3metres long etc etc. Based on the information you have given there doesn't appear to be a problem. It is likely that this has been done due to 95mm solid cores not making a good connection to the mccb terminals.
Also the internal wiring of a panel is most likely subject to different regulations.

With the eddy current problem, are you sure the glands have to been insulated from each other at one end or had slots cut at one end?
 
Where the entire run of the circuit is suitable for the protective device then there is no need to add additional protection at any reduction in csa since it is already protected at origin.
If there is a reduction is csa such that the cable is no longer protected by the protective device then another protective device, that does protect the reduced csa conductor, should be placed in circuit.
 
Eddy currents are not normally a problem in cables carrying less than 200a....as this is a 100a supply it shouldn't be an issue.

Is this definitely true? I would have thought a 100A circuit could have problems with eddy currents if plate not slotted. Daz
 
Eddy currents are not normally a problem in cables carrying less than 200a....as this is a 100a supply it shouldn't be an issue.
This is the general concensis although you should still takes measures to prevent it, i the OP case the set-up will be affected by Sheath eddies and these will exaggerate the effect and can cause issue at lower ampage .... I've come across a switch bank with 3 phase supply entering through different metal conduits (2/1split) which commoned on the M/C switch and the steel trunking 1m above... with <20amps in load per phase the conduits were too hot to touch and starting to exceed the limits of the 70'c singles insulation... all you require is the effect to start and heat disappation to be slow and you get a runaway effect even at low ampage.

The 200amp rule is where is becames an issue in most circumstances regardless and just explains why you may not see its effects at lower levels but we mustn't get complacent over the rarer occasions that it is an issue <200amps because under the right conditions its just as dangerous.
 
Last edited:

Reply to obscure regs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've got a bunch of old single phase BS88 1970s fuseboards in the communal areas of a converted building. All the wiring is MICC and it's buried...
Replies
9
Views
1K
Hello all, visit to site today to see in an install of a 315A 400V supply to a machine. Client mentioned previously they were going to use single...
Replies
12
Views
4K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
78K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock