Discuss Off Grid in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Im going to give NAPIT tech support a call later today but thought id try to get some other expert opinions too.

Ive just carried out a EICR on a remote property in the Welsh borders. Its a new installation and new build ECO friendly house which has been built over 4 years with the electrical installation carried out by the owner under 'some' control by a local electrician. the electrician has not been able to test it however as he does not have third party registration. I spoke to local building control who basically said it was up to me whether to carry out a new installation cert or EICR. I went for EICR as more thorough.

My query is about the supply system i should enter on the cert. It is entirely off grid powered through PV arrangement with back up generator which kicks in when batteries drop below 45%. both feed in to the inverter equipment which contains the interlock switching to prevent both supplies being energised at the same time. It is a self contained system which has been certified by the installer with no earth connection to any public distributors supply. The owner has installed 2 x earth electrodes connected to a main earthing bar which has a solid link to Neutral at the point of source. From there all earthing is in seperate earths and CPCs

All readings are good with 137 ohms through the mass of earth between the electrodes and a Ze of 0.86 ohms at the consumer units. All circuits give v good results. so finally to the question. Do i enter TNS for this system on the Cert or could it be classed as IT?
Many thanks for reading....
 
If it has a solid link to the neutral bar I can't see how it can be TNS I would of thought it is a TNCS.

Would you be able to sketch it out or put up a couple of pictures ?
 
Last edited:
Yes, I have thought about that, and didn't really read it correctly.

On our supplies that come from our HV transformers (no other customers connected) we have them as PNB this is indeed a type of TNS.
 

Reply to Off Grid in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock