Hi all,

I'm hoping someone on here can shed some light on an issue I currently have with a bedroom light switch.

Yesterday evening, I attempted to change the standard light switch in one of the spare bedrooms for a dimmer switch. I initially swapped each wire, like for like, so that the COM's wire from the old switch was put into the COMs terminal of the new dimmer switch and so forth.

With the electricity turned back on, everything seemed fine, as the dimmer switch was working as intended, however, I soon discovered that the lights in my bedroom, en-suite and walk in wardrobe were acting up, as they'd either fail to turn on or began to flicker when they did work etc. Unsure what might be causing this issue, I decided to cut my losses and just refit the old switch, believing everything would go back to as it was before I had decided to meddle with it.

It was at this point that I realised that the L2 terminal had been removed (see photo) from the original switch, which would probably make sense, as it is just a 1 way switch, but what I'm now wondering is what the third wire is for? Where should it go? It was originally just pushed into where the L2 terminal would be. Despite this, I refitted the switch as it was originally and the light is working fine, but now none of the lights in my bedroom are working. If I swap the wire in L1 terminal for the one that's sitting in the empty L2 terminal, the switch no longer works in the spare room, but turns on the lights in my bedroom. I'm totally at a loss as to why the switch will no longer work as it had originally.

If anyone has any idea how I can rectify the issue and if possible, install the new dimmer switch, I would be eternally grateful :) Failing that, I'll settle for leaving the old switch on the wall.

Cheers

Steve
 

Attachments

  • IMG_20220110_121434.jpg
    249.4 KB · Views: 81
  • IMG_20220110_121444.jpg
    246 KB · Views: 78
  • IMG_20220110_121857.jpg
    234.5 KB · Views: 75
A third brown wire suggests a looped feed to another switch. Using the original switch, connect 2 browns to COM and one to L1
Nothing should have been in L2

Any of the following may happen.

1. You got it all right! Congrats.
2. The bedroom light is always on. The spare room doesn’t work until you turn on the bedroom.
3. Neither the bedroom or the spare room work until you turn on the switch


With only 3 browns, there’s a limit to how it can go. Mark them with sharpie pen 1 line, 2 line and 3 lines. Connect them 1 and 2 in COM, 3 in L1.
Off that doesn’t work, swap 2 and 3
 
A third brown wire suggests a looped feed to another switch. Using the original switch, connect 2 browns to COM and one to L1
Nothing should have been in L2

Any of the following may happen.

1. You got it all right! Congrats.
2. The bedroom light is always on. The spare room doesn’t work until you turn on the bedroom.
3. Neither the bedroom or the spare room work until you turn on the switch


With only 3 browns, there’s a limit to how it can go. Mark them with sharpie pen 1 line, 2 line and 3 lines. Connect them 1 and 2 in COM, 3 in L1.
Off that doesn’t work, swap 2 and 3
Connected two of the wires to the COM terminal and the third to the L1, as suggested and it worked first time round.

Cheers, littlespark.
 
it's only if 1 wire is in L2 that you have to turn it upside down. if using C and L1. either way round nothing really matters.


 

Reply to One Way Switch Issue. Help! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock