Discuss Out building earth in the Electricians' Talk area at ElectriciansForums.net

I take it then Malcolm that you do not accept that you should first contact the DNO before exporting a TN-C-S earth, and that you would be quite suprised if they were to disconnect your supply, or just remove the PME connection after discovering that youhad exported such an earth without their permission?

If you read my OP in yesterdays thread you would see that as I'm old school and still remember the old ELecticity safety Regulations where there was a PME section included. I'm very much in favour with contacting the DNO about exporting earths but as I related the chances are the DNO will be be amazed you have contacted them regarding this in 2011.

But I have not mentioned exporting earths I was wondering why you are bringing DNO values into a domestic installation.
 
I'm not particuarly bringing DNO values into a domestic installation.
Somebody brought up installing a rod along with exporting a TN-C-S earth.
Doing such would effectivly make that rod one of the multiple earths.
As such the DNO's often have particular requirements for such situations, and can get quite shirty about it.
 
Sorry. 542.1.1

This mentions you can connect to one of the types of earthing system.
This states that the main earthing terminal shall be connected with earth by one of the methods described etc.
Those methods being TN-S, TN-C-S and TT.
If you were then to read further, you would come across Regulation 542.1.5 "The earthing arrangements may be used jointly or separately for protective and functional purposes according to the requirements of the installation".
As I said there is nothing in either BS771 or ESQCR prohibiting this.
 
I have never,ever heard of the DNO getting uppity over a TNCS earth exported to an outbuilding,and I have never contacted them before doing so....In my experience all they are interested in is a cert saying it complies with bs 7671.

Simplified....
1.There are no regulations in Bs 7671 preventing a TNCS earth being used as the earthing system for an outbuilding..(except in some special locations as defined in bs 7671)
2.If there are extraneous conductive parts within the outbuilding that require main bonding then the requirements for bonding TNCS installations apply. This would mean a minimum 10mm bonding conductor would have to be installed from the outbuilding back to the MET. This may be impractical or it may not be cost effective.It may be cheaper to separate the TNCS earth and install a rod,in which case main bonding can run to the outbuilding DB.
3.If there are no extraneous conductive parts within the outbuilding requiring main bonding using the TNCS earth is in full compliance with bs 7671. As long as you carry out and cert the install to bs 7671 there is no need to contact the DNO.

That is how I've been doing it for 30yrs,and that is in full compliance with all relevant regulations.

If you are not in agreement....well, do it your own way:cool:
 
Last edited by a moderator:
I have never,ever heard of the DNO getting uppity over a TNCS earth exported to an outbuilding,and I have never contacted them before doing so....In my experience all they are interested in is a cert saying it complies with bs 7671.

Simplified....
1.There are no regulations in Bs 7671 preventing a TNCS earth being used as the earthing system for an outbuilding..(except in some special locations as defined in bs 7671)
2.If there are extraneous conductive parts within the outbuilding that require main bonding then the requirements for bonding TNCS installations apply. This would mean a minimum 10mm bonding conductor would have to be installed from the outbuilding back to the MET. This may be impractical or it may not be cost effective.It may be cheaper to separate the TNCS earth and install a rod,in which case main bonding can run to the outbuilding DB.
3.If there are no extraneous conductive parts within the outbuilding requiring main bonding using the TNCS earth is in full compliance with bs 7671. As long as you carry out and cert the install to bs 7671 there is no need to contact the DNO.

That is how I've been doing it for 30yrs,and that is in full compliance with all relevant regulations.

If you are not in agreement....well, do it your own way:cool:


Sounds bang on to me.:)
 
just a qusetsion fellas, im currently working on a job where we are installing lighting and power to metal kiosks, above well heads for a water board. they are having us take a supply from a panel in the main plant building, (3c10mm2 swa). we have been told to bond the armour at both ends, and to terminate the earth in the kiosk CU as normal. we are also installing an earth rod to each kiosk, which is then connected to the CU, either directly, or via an earth bar.

What is your take on this?

A lad earlier posted about a reg saying this is permitted, but i haven't got a copy of the regs to refer to.

I think that it is fine, as it is no different practicaly speaking, to bonding services, which can act as earth electrodes, or bonding to lighning protection, which uses earth electrodes?

Im just seeking some confirmation please?

John
 

Reply to Out building earth in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
Replies
12
Views
2K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Minimum requirements for earthing a steel framed shed? 4x3m As3000 once again giving conflicting advice.. Incoming submain 6mm TPS 2 Core plus...
Replies
3
Views
1K
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock