Discuss Out building earth in the Electricians' Talk area at ElectriciansForums.net

I take it that one of the cores will be used as an earth conductor?
Have they given you any instructions rgarding the earth rod resistance, or just asked you to bang one in?
 
Just a quickie ....... If the house is T T and the garage at the bottom of the garden is of wooden construction with a concrete floor, steel up-&-over door, one flossie light & 2 twin 13A sockets, am I right in thinking that it should be fed from the house in 2 core SWA with the SWA connected to earth at the house end only, and a spike provided at the garage to earth the CU in the garage?

Many thanks.

(sorry to be a pain)
 
Last edited by a moderator:
Just a quickie ....... If the house is T T and the garage at the bottom of the garden is of wooden construction with a concrete floor, steel up-&-over door, one flossie light & 2 twin 13A sockets, am I right in thinking that it should be fed from the house in 2 core SWA with the SWA connected to earth at the house end only, and a spike provided at the garage to earth the CU in the garage?

Many thanks.

(sorry to be a pain)

I can see no reason to do this,I would use the main earth,although both methods are permitted.
411.5.1
 
hmmm . if the house is TT, is there any reason not to bring the earth from the house ( as a 3rd core) and bang in a rod at the outbuilding as well. thus possibly bringing down the Ze for both the house and otbuilding?
 
Just a quickie ....... If the house is T T and the garage at the bottom of the garden is of wooden construction with a concrete floor, steel up-&-over door, one flossie light & 2 twin 13A sockets, am I right in thinking that it should be fed from the house in 2 core SWA with the SWA connected to earth at the house end only, and a spike provided at the garage to earth the CU in the garage?

Many thanks.

(sorry to be a pain)

Yes this would be the best option, as the local earth at the garage could have a potential difference to that of the local earth at the installation electrode.
 

Reply to Out building earth in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
Replies
12
Views
2K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Minimum requirements for earthing a steel framed shed? 4x3m As3000 once again giving conflicting advice.. Incoming submain 6mm TPS 2 Core plus...
Replies
3
Views
1K
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top