Discuss Outdoor Lights & Water Feature Setup in the UK Electrical Forum area at ElectriciansForums.net

N

Neadles

Gents, just want some advice on the domestic side as I'm more an industrial engineer. I have 4 lights and a small water feature going to be remotely switched in my new landscaping project (joys of working shifts time for home improvements instead of tinkering with my track car!). I can get easy access to my CU I just want to know what would be the best option of running a supply:

1. RCD fed side with just an 6A MCB or
2. Non-RCD supplied side with a 6A RCBO to stop nuisance tripping

I do have a spur RCD FU but with out changing the main RCD in the CU I will not have proper discrimination so I'm thinking that RCBO is the way as that's what we tend to do at work with all our annoying lighting circuits outside?

Cheers
 
RCBO off the non-RCD side of the CU is definitely the way to go. any fault outside will only trip it's own RCBO.
 
anything outside, with the exception of cable on the building fabric. i'd fit RCD protection. OK, it's not sockets, but you have to allow for idiots. if SWA is used, there'll still be connections to flexes.
 
Thanks for the the quick reply's.

Well I hadn't thought that far yet but there is some existing plastic conduit running from another installation that I was going to utilise, basically it was concreted in with the new drive and garage and takes a welding supply to the garage, I was going to feed some flex I had at work that was in the skip 1.5mm from a contractors lighting job we had done. Am I wrong in thinking then this will be ok with the additional mechanical protection instead of SWA? I am bassically planning on sticking 4 brick lights in a small wall near the garage which will have conduit upto it through the wall to the light fitting in the wall? The water feature has a round cable with a plug on it, designed for purpose obviously, that I will just joint into one of the switch units.

Should it really all be SWA and if so on all the domestic IP6* rated items there all plastic so that would mean joining all the out armours together and back to the supply earth. Am I wrong in thinking if the supply in the house is protected prior to going outside, is the cable ok along as it is sufficiently burier with additional mechanical protection?

Please feel free to correct me I have read the 17th addition and done the course to try and get up to speed, but to honest domestic installations especially outdoors are not my speciality as I don't do it from day to day.
 
i would feed from CU RCBO in T/E, out the wall into an adaptable IP rated box. from there SWA to wherever you are fitting lights, etc. then fit a IP rated socket for the water feature ( i use remote control ones from byron). the light can be spurred off the socket ( fused down if reqd.) ans also remotely switched.
 
i would feed from CU RCBO in T/E, out the wall into an adaptable IP rated box. from there SWA to wherever you are fitting lights, etc. then fit a IP rated socket for the water feature ( i use remote control ones from byron). the light can be spurred off the socket ( fused down if reqd.) ans also remotely switched.

Cheers for all that pretty much what I am going to do, all the cable will be in conduit and under 6" of concrete and stone and after all the digging isn't every coming up again!


Just another quick question on outdoors if you don't mind? On requirments of cables, if it is to be buried in concrete does it only have to be 6" deep in a conduit (does it matter if its SWA) and if under soil 450mm in SWA?
 
under concrete and unlikely to be disturbed, you'll be OK. if you're going to use flex in conduit, then get some hi-tuf.
 

Reply to Outdoor Lights & Water Feature Setup in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
894
Im just curious as to peoples thoughts on the following install I seen on a video from an Electrical firm today and they did the following: Ran...
Replies
2
Views
522
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
659
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock