- Reaction score
- 67,272
richard is spot on. 1. it's not notifiable. 2. the cable through the wall does not fall within the remit of 522.6.101. that refers to cable buried below plaster and prone to being nailed or screwed into.
fit a FCU, then flex to the light. either use the FCU as a switch, or fit a switch somewhere convenient. if you do have to chase cable in, then fir a RCD FCU. test and complete a MWC.
fit a FCU, then flex to the light. either use the FCU as a switch, or fit a switch somewhere convenient. if you do have to chase cable in, then fir a RCD FCU. test and complete a MWC.