- Reaction score
- 8,896
A strange small job this afternoon.
Stoves oven : another sparks had proclaimed the element was faulty and causing the RCD to trip. Householder had already purchased a new element. The original sparks has since been unwell. Slight suspicion crept in that I'd find wires dropped down the back, or that the whole range needed pulling out.
But no, I turn up, remove old one, test it, and get 27.6 ohms, and open circuit from both terminals to earth.
I test new one, and get the same.
At this point I share my doubts with customer, and ask if I can have a nose at the dual RCD consumer unit, suspecting a N-E fault that the oven is driving current through. Unfortunately the consumer unit had been boxed in to the extent I couldn't get the front off.
We agree I'll change the element anyway which on the face of it seemed to work. No sign of tripping after 5 minutes.
It then occurs to me I can ramp test the RCD from a socket on the same side of the board, and do this - it took 25ma to trip it.
So at this point there is no sign of fault at all, and 5ma leakage, giving me some confidence that it's not about to trip.
Can an element measure a normal resistance and still be faulty?!
If not it must be something that is on a plug top or downstream of a double pole isolator that is the actual problem.
I have a feeling I haven't heard the last of this one.
Stoves oven : another sparks had proclaimed the element was faulty and causing the RCD to trip. Householder had already purchased a new element. The original sparks has since been unwell. Slight suspicion crept in that I'd find wires dropped down the back, or that the whole range needed pulling out.
But no, I turn up, remove old one, test it, and get 27.6 ohms, and open circuit from both terminals to earth.
I test new one, and get the same.
At this point I share my doubts with customer, and ask if I can have a nose at the dual RCD consumer unit, suspecting a N-E fault that the oven is driving current through. Unfortunately the consumer unit had been boxed in to the extent I couldn't get the front off.
We agree I'll change the element anyway which on the face of it seemed to work. No sign of tripping after 5 minutes.
It then occurs to me I can ramp test the RCD from a socket on the same side of the board, and do this - it took 25ma to trip it.
So at this point there is no sign of fault at all, and 5ma leakage, giving me some confidence that it's not about to trip.
Can an element measure a normal resistance and still be faulty?!
If not it must be something that is on a plug top or downstream of a double pole isolator that is the actual problem.
I have a feeling I haven't heard the last of this one.