ukpablo
cheers bud, did this but took off biggest fuse, multiplied the rest by 0.4 and added biggest fuse back on.
this is what the board had connected
6A lights
6A lights
32A radial for panel heaters
32A cooker(3KW)
32A hob (3KW)
32A ringmain
32A ringmain
16A water heater
16A skts radial
40A shower (9.5 KW)
16A whirlpool bath
total was 128A
main switch was 80A
main fuse was 60A.
thanks anyway
also connected was 6 x 16A mcb on seperate board for storage heaters........did not calc these.
this is what the board had connected
6A lights
6A lights
32A radial for panel heaters
32A cooker(3KW)
32A hob (3KW)
32A ringmain
32A ringmain
16A water heater
16A skts radial
40A shower (9.5 KW)
16A whirlpool bath
total was 128A
main switch was 80A
main fuse was 60A.
thanks anyway
also connected was 6 x 16A mcb on seperate board for storage heaters........did not calc these.