Try not to do PA Testing but had to do it today!

Was doing the above today after a cottage got flooded. Lead didn't appear to be wet, but failed the insulation test @ 0.7Mohms, this was at a test voltage of 250V.

Re-tried it with my installation tester at 100V and 50V and got the same readings. I thought a surge protector should pass insulation testing if test voltage is 250V or less, or am I being dumb, or is the lead really duff?
 
Surge protected extension leads should pass an insulation Resistance test at 250V, generally they bypass to earth at about 400V so a 500V test will fail (and possibly negate the surge protection).

I would say that the lead was damaged in some way, possibly it had taken a surge before and is now dead.
 

Reply to PA Testing surge protection extension lead in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
989
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
994
I had a fault finding job on Thursday, intermittent RCD tripping. 2 actually, there was a 30mA RCD upstream, and a 30mA RCBO protecting the...
Replies
4
Views
5K
Hello all, I am new to PAT testing and have a Fluke 6500-2. I am having an issue whereby I cannot seem to drop the voltage down to 250V when...
Replies
2
Views
2K
Hi all, This has got me stumped as it's the first time in 8 years this has happened. I undertook a 250v test on a brand new recently purchased...
Replies
11
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock