So when doing partial testing, when doing ring circuits i have a query.

Do end to end prove each conductor is a ring. In the area on the test sheet it says r1+r2 OR r2. Is it ok to do end to end and fill in the cpc end to end reading (r2) into this box and do zs of every socket to not only get a zs reading but also prove continuity as the tester alerts to mixed polarity.
 
youse confused r1, r2,rN are end to end. R1+R2 or R2 are different.e.g. R2 will be using a wander lead to each point, recording the highest. for a ring generally, R1+R2 = (r1+r2/4)
 
Why would you only do partial testing? If the circuit is locked off then I would do the full lot of dead tests.

Measuring CPC end to end and dividing by four will not confirm earthing connection at each point or polarity.
 
Why would you only do partial testing? If the circuit is locked off then I would do the full lot of dead tests.

Measuring CPC end to end and dividing by four will not confirm earthing connection at each point or polarity.
Partial testing would not be acceptable for initial verification, but is acceptable on an EICR. For example if a measured Zs reading is comparable to the measured Zs recorded on the original EIC then it would be reasonable to assume the R1+R2 will also be comparable, and so not carry out that test.
So that's why you might only do partial testing.
 
Partial testing would not be acceptable for initial verification, but is acceptable on an EICR. For example if a measured Zs reading is comparable to the measured Zs recorded on the original EIC then it would be reasonable to assume the R1+R2 will also be comparable, and so not carry out that test.
So that's why you might only do partial testing.
I agree but on a ring final how would you confirm polarity at each point and identify any crossovers without fully dead testing?
 
My company is a social landlord. We do partial testing if we have existing certificates of an installation.

I confirm polarity of each socket on a ring by doing a zs reading at each socket. Any polarity issues my tester wouldnt start the reading and beep at me the issue. So by doing end to end then zs at each point i confirm its a complete ring amd each point is correct polarity wise
 
Obviously full testing is better on a RFC but if you really must do partial testing on a RFC I would obtain the R1+R2 by doing the end to ends, adding them together then dividing by four, as said above. Just an R2 value on a RFC doesn't quite seem right.
 
I dont just do an r2 reading. I do end to end to confirm the ring then do zs at each one
Stupidly i was thinking that where it says r1 r2 or r2 i could jusy put the cpc end to end in...but after i posted i realised this result was the r2 from say using the wandering lead.

In regards to the IR i do if i need to do a full test or the circuits are not on the rcd side.
 
I agree but on a ring final how would you confirm polarity at each point and identify any crossovers without fully dead testing?
As above Zs testing will confirm polarity. Full dead testing on a RFC is very time consuming and disruptive if the layout of the circuit is unknown. R1+R2 readings will be skewed by spurs, and identifying spurs from spurs will involve considerable dismantling.....I use my judgement to decide whether a RFC has issues that need further investigating or commenting on after end to end, IR and Zs tests.
None of the above applies to initial verification in which the layout of the RFC should be known and full testing must be carried out.
 
[QUOTE="magnoliafan89, post: 1506944, member: 98919
In regards to the IR i do if i need to do a full test or the circuits are not on the rcd side.[/QUOTE]

No IR testing at all on any RCD protected circuits?
 
No. I do 4 eicr a day. I do 10% of the installation so i do ze pfc check bonds do rcd time and pick 2 circuits to test i always pick one socket circuit and maybe another or a shower or light whatever i can do in the time i have.
 
Like i said if a circuit or circuits dont have rcd protection i will do IR. The majority of our properties have been rr wired in the last 20 years. None our wired before 85. Theres always a full test done within the last 10 years so if there was any deteroiation im sure it would be quite apparent.
 
This is simply not true, the IR can be below the allowed value without the rcd tripping. It is just lazy not to do it.
On an EICR you only have do L&N to CPC so why not do it
 
These houses are very much lived in and cluttered to absolute buggery i have 2 hours in which to do the eicr im not going round unplugging absolutely everything!! Taking out all the lamps and disconnecting all fire alarms just to get an accurate reading.
Its not lazy im trying to do the best with what little time i have.

If i wanna say to my company hey im not happy with doing it this way even though you have been told by the niceic you can do this...im sure there response will be well good luck with your next job.
A luxury i cannot afford to do at the moment. So jump down off your high horse i will not be called lazy when im rushing like mad to get these things done in the time im alloted.
 
You ever done say a boiler circuit ln to e....i have without disconnecting it...got a false reading disconnected it got over 2Mohms same with a lighting circuit before now. Usb sockets have given me funny readings before now. I used to do the IR until i was told to speed it along and if its rcd protected dont bother.
Sorry but calling me lazy and being like that was quite rude.
 
Long as you feel like you have done a full and proper job testing an install for the safety of the tenant and are happy signing the cert carry on.
FYI I don’t seem to be able to test more than 2 properties in one day, maybe I just crap
 
Long as you feel like you have done a full and proper job testing an install for the safety of the tenant and are happy signing the cert carry on.
FYI I don’t seem to be able to test more than 2 properties in one day, maybe I just crap

I do not like having to do partial tests im much happier to do 1 full on thorough test in a day. But when i do them i do make sure they are as thorough as i can make them and i make sure rhe install is safe. I have on occasion called the office to cancel my next appt so i can repair any faults/damage non compliance etc
I write all limitations downand also if i feel the property is in need of a re wire or anything such as a CU upgrade i will put at the bottom of sheet 1 my advisorys. In that sense my company has sent me to give my opinion, i have tested the property and i am issuing them a certificate with what i feel needs to be follow on work...whether they then act on it...
Im off...i have a night of sexless passion to get on with happy thursday
 

Reply to Partial testing and R1+R2......... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Have only recently gotten in to testing. Doing an R1+R2 on a lighting circuit but instead of producing a result my tester clicks over and over...
Replies
5
Views
951
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
895
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top