Did the job today - it wasn't an official PAT test, more a safety check on an appliance that may or may not work. The appliance was passed on to owner as a spares or repair project because it had previously failed an earth bond test when another company PAT tested it. I soon sorted that problem out - no earth connection because where flex was connected to the machine, the earth connector was gripping the insulated part of the ferrule instead of the uninsulated part of it. Had probably been like this from the factory! Official PAT test is to be completed once appliance is up and running - owner has not got a 415V socket in his installation at the moment.
I bought a 32A connector socket but didn't use it in the end. Didn't use the Fluke 6500 either. Opened up the plug to see how it was wired and to check connections. Then checked the earth bond with Megger 1552. Then clipped the three phases together (there was no neutral), and put one test lead on phase and one test lead on earth, and IRed first at 250V then at 500V. Was satisfied enough with results to not throw 1000V at it. Was unable to run it to do load test because supply not available yet.
In writing this I realised I should have wired a 13amp plug to the 32A connector and done a proper Earth Bond at 25A with the Fluke 6500. Will go back and do this tomorrow.
connections for 32A connector to 13A plug:
(32A) L1+L2+L3 --> (13A) L
(32A) N --> (13A) N
(32A) E --> (13A) E
This for Earth Bond and IR test using Fluke 6500.
Note for IR test - always check internal wiring on appliance plug to ensure wired as expected.
Also need another 32A connector socket and 32A plug to make up a mini extension lead
L1 --> L1, L2 --> L2, L3 --> L3, N --> N using four-core flex
E --> E in single run parallel to the flex, but with some slack.
That way can put a clamp meter round the earth and measure earth leakage when the appliance is running. Will not be able to do full load test because unable to measure drawn power. Could possibly wire this lead completely in singles and group together L1+L2+L3 so can measure drawn current, then calculate power consumption.
Ideally would also have another 32A plug connected to a C13 IEC female
(32A) L1+L2+L3 --> (C13) L
(32A) N --> (C13) N
(32A) E --> (C13) E
this to be used in conjunction with the first lead above (the Earth Bond and IR lead) to test 415V extension leads
That's a lot (about £50 worth) of 32A connectors/plugs to buy!
Of course, all readings obtained need to be interpreted making reference to the Code of Practice.
Detailed this as a sort of reminder to self and hopefully help others unsure how to test 415V appliances.
All above is based on my own assumptions about how to do this properly, and I stand to be corrected if any of it is incorrect or could be done better.