Hi All,

I understand the requirement for PEN fault detection on EV chargers for TN-C-S installs (or to place an earth rod). However, when I was looking for something else entirely I came across this single-phase 100A PEN fault detector. What would be the use case for this? Would you ever need to (or want to) protect a whole domestic install with one of these?

Matt:e Single Phase Auto Reset PEN Fault Protection with 100A MCB

Thanks for your thoughts
A.
 
Hi All,

I understand the requirement for PEN fault detection on EV chargers for TN-C-S installs (or to place an earth rod). However, when I was looking for something else entirely I came across this single-phase 100A PEN fault detector. What would be the use case for this? Would you ever need to (or want to) protect a whole domestic install with one of these?

Matt:e Single Phase Auto Reset PEN Fault Protection with 100A MCB

Thanks for your thoughts
A.
Presumably the design intention of it is for supplying multiple chargepoints, though it seems somewhat unrealistic to connect 100A of EV charging capacity to a single phase supply.
 
The main use for an open-PEN system in my mind are situations where you cannot safely allow the CPC to be used due to shock risk, but also you are not in a position to TT earth the load(s) or whole installation (e.g. no safe / practical rod location, or bonded utilities still espose you to the PEN connection).

There is a good argument that for most purposes TN-C-S (with its attended risk of open-PEN fault) is still safer than TT with the reliance on (in many cases a single rarely-tested) RCD for fault disconnection. But clearly some cases that is not the case so you need either this sort of a box, a TT supply, or an EV charger that has the open-PEN fault protection built in.
 

Reply to PEN Fault Detection on Whole Install? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Can we as electricians pick up on a broken PEN conductor? I’ve installed an EV charger for FIL, and everything tested fine, but there is a fault...
Replies
8
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
732
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I've installed a Tesla Gen 3 wall charger supplied by my client. For your information, the place that I installed is in a block of flat...
Replies
2
Views
1K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock