two collages same tutor in week .. sat tutor is someone else who gives out alot of sheets and other useful info the weekly chap is not very helpful just wants everyone to look on net and find the answers..
 
tend to agree,

A CODE 2 For labels which are not attached to the db i think is very harsh, there is no way i would fail an installation because of this, i would put that down as a code 4.

however a good reference guide as you said :)
 
I would use the Safety council codes at the moment but attachement added showes proposed new PIR form now EICR from BSI website BS7671 proposed Amendment 1 now only 3 codes not 4
 

Attachments

  • BS_7671_Amendment_1.pdf
    820 KB · Views: 660
Quite like the look of the possible new codes. Was doing remedial work from a PIR a few weeks back and the spark that did it had no schedule of circuits as a code 1:eek:

Code 3 on the new report is a bit open though.
 
Hi confused-fuse,

I have a word document on codes which I hope may help a bit, cant find a way of attaching it and have to do in in two parts(?) due to word length, sorry...so here as follows:

Understanding Codes in Periodic Inspection Reports.

Each observation in a Periodic Inspection Report must be given an appropriate recommendation Code 1,2,3 or 4 as summarised in the following table.

Code Meaning

1 Requires urgent attention
2 Requires improvement
3 Requires further investigation
4 Does not comply with BS7671 (as amended); this does not imply that the electrical installation is unsafe

Where a real and immediate danger is observed, recommendation Code 1 must be used.

Where one or more observations are given as Code 1 or 2, the overall assessment of the installation should be stated to be UNSATISFACTORY in the Periodic Inspection Report.

Code 1 – Indicates that the observed deficiency requires urgent remedial action to bring the standard up to a level that complies with BS7671.

Examples:-

1. Exposed live parts that are accessible to touch, such as where:
a. A fuse carrier or circuit breaker omitted from a consumer unit and a blanking piece is not fitted in its place.
b. Terminations or connections have no (or damaged) barriers or enclosures, such as those belonging to a consumer unit.
c. An accessory is damaged.
d. Live conductors have no (or damaged) insulation.

2. Conductive parts that have become live as the result of a fault

3. Absence of an effective means of earthing for the installation.

4. The main RCD or voltage-operated earth-leakage circuit-breaker on a TT system fails to operate when tested with an instrument or integral test button.

5. Evidence of excessive heat (such as charring) from electrical equipment causing damage to the installation or its surroundings.

6. Incorrect polarity, or protective device in neutral conductor only.

7. Circuits with ineffective overcurrent protection (due, for example, to oversized fuse wire in rewireable fuses).

8. Absence of RCD protection for socket-outlets in bathrooms or shower rooms other than SELV or shaver socket-outlets.

9. Socket-outlets other than SELV or shaver socket-outlets located within 0.6 metres horizontally from the boundary of zone 1 in a location containing a bath or a shower.

10. Absence of earthing at a socket-outlet.

Code 2 (Require Improvement) – Indicates that the observed deficiency requires action to remove potential danger, as soon as possible to bring the standard up to a level that complies with BS7671.

Examples:-

1. a 30/32 A ring final circuit discontinuous or cross connected with another circuit.

2. A public utility water pipe used as the means of earthing for the installation.

3. A gas or oil pipe being used as the means of earthing for the installation.

4. Absence of circuit protective conductors for a lighting circuit supplying one or more items of class 1 equipment.

5. Absence of main equipotential bonding (except to a lighting protection system conductor, where a recommendation code 3 may be appropriate).

6. Absence of fault protection by RCD (protection against indirect contact / fault protection) where required, such as for a socket-outlet circuit in an installation forming part of a TT system.

7. A ‘borrowed neutral’, for example where a single final circuit neutral is shared by two final circuits (such as an upstairs lighting circuit and a separately protected downstairs lighting circuit).

8. Absence of a warning notice indicating the presence of a second source of electricity, such as a micro-generator.

9. Fire risk from incorrectly installed electrical equipment including incorrectly installed recessed down-lighters.

10. Undersized main bonding conductors, where the conductor is less than 6mm² or where there is evidence of thermal damage.

11. Unenclosed connections at luminaires not enclosed (such a defect can contribute to a fire, particularly where extra-low voltage filament lamps are used).
12. Immersion heater does not comply with BS EN 60335-2-73 (that is, does not have a built in cut-out that will operate if the stored water temperature reaches 98º C if the thermostat fails), and the cold water storage tank is plastic.

13 Unsatisfactory functional operation of equipment where this may result in danger.

14 Socket-outlets other than SELV or shaver socket-outlets located between 0.6 metres and 3 metres horizontally from the boundary of zone 1 in a location containing a bath or shower.

15 Absence of RCD protection for portable or mobile equipment that may reasonably be expected to be used outdoors.

16 Earth fault loop impedance value greater than that required for operation of the protective device within the time prescribed in the version of BS 7671 / IEE Wiring Regulations current at the time of installation.

17 Insulation of live conductors deteriorated to such an extent that the insulating material readily breaks away from the conductors.

18 Neither local supplementary bonding (where necessary) nor RCD protection is present in a bathroom or shower room. Note: where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test.

19 Anyone circuit has an insulation resistance of less than 20 kilo ohms.

Hope this is of some help,

Best wishes

Rex
 
Hi confused-fuse,
second bit...


Code 3 (Requires further investigation) – Indicates that usually the inspector was unable to come to a conclusion about this aspect of the installation or the observation was outside the agreed purpose.

Examples:-

1 Unable to trace final circuits

2 Unable to access equipment or connections needing to be inspected that are known to exist but have been boxed in such as by panels or boards that cannot be easily removed without causing damage to decorations.

3 Insulation resistance of less than 1 mega ohms between live conductors connected together and earth, when measured at the consumer unit with all final circuits connected. If any one circuit has an insulation resistance of less than 20 kilo ohms, a code 2 recommendation should be given.

4. Absence of a main equipotential bonding connection to a lighting protection system conductor, where it is not known by the inspector if it is required to protect against lightening side flashes. (Absence of other main equipotential bonding connections would usually warrant a code 2).

Code 4 (Does not comply with BS 7671 as amended)

Examples:-

1. Switch lines not identified as line conductors at terminations (for example, a conductor having blue insulation is not sleeved brown in switches or lighting points).

2. Circuit protective conductors or final circuit conductors in a consumer unit not arranged or marked so that they can be identified for inspection, testing or alteration of the installation.

3. Undersized main bonding conductors (subject to a minimum size of 6mm²), if there is no evidence of thermal damage.

4 Absence of circuit protective conductors in circuits having only Class II (or all insulated) luminaires and switches.

5 Protective conductor of a lighting circuit not (or incorrectly) terminated at the final circuit connection point to a class II (or insulated) item of equipment, such as at a switch mounting box or luminaire.

6 Absence of ‘Safety Electrical Connection – Do Not Remove’ notice.

7 Absence of a notice indicating that the installation has a wiring colours to two versions of BS 7671.

8 Absence of RCD periodic test notice

9 Absence of circuit identification details

10 Sheath of an insulated and sheathed non-armoured cable not taken inside the enclosure of an accessory, such as at a socket-outlet or lighting switch.

11. Bare protective conductor of an insulated and sheathed cable not sleeved with insulation, colour coded to indicate its function.

12 Installation not divided into an accurate number of circuits to minimise inconvenience for safe operation, fault clearance, inspection, testing and maintenance.

13 Fixed equipment does not have a means of switching off for mechanical maintenance, where such maintenance involves a risk of burns or injury from mechanical movement

14 Absence of supplementary bonding to installed Class II equipment where required (such as in a bathroom or shower room, in case the equipment is replaced with Class I equipment in the future).

15 Reliance on a voltage-operated earth-leakage circuit-breaker for fault protection (protection against indirect contact – fault protection).

16 Absence of RCD protection for cables installed at a depth of less than 50 mm from a surface of a wall or partition where the cables do not incorporate an earthed metallic covering, are not enclosed in earthed metalwork, or are not mechanically protected against penetration by nails and the like.

17 Absence of RCD protection for cables concealed, at whatever depth, in a wall or partition the internal construction of which includes metallic parts (other than metallic fixings such as nails, screws and the like) where the cables do not incorporate an earthed metallic covering are not enclosed in earthed metalwork, or are not mechanically protected to avoid damage to them during construction of the wall or during their installation.

18 Absence of RCD protection for socket-outlet circuits that are unlikely to supply portable equipment for use outdoors, or that are in a bathroom.

19 Absence of supplementary bonding where required, such as in a bathroom or shower room, where all the following three conditions are not satisfied:

a all final circuits of the location comply with the requirements for automatic disconnection, and

b all final circuits of the location have additional protection by means of a 30 mA RCD, and

c all extraneous-conductive-parts of the location are effectively connected to the protective equipotential bonding (main earthing terminal).


Source: NICEIC Domestic Periodic Inspection, Testing and Rep
 
Thes codes are a complete waste of time they are open to imterpretation by who ever is testing, if you give a PIR to a client and tell them the codes indicate whats needed,how the hell can he tell whats important, the only people remotely interested is your yearly assesor. I mean, come on almost every installation will have a 4 you can apply that to any thing you like from a cracked face plate to a rewireable with a piece of coat hanger between the termnial screws and page 2 is often not big enough
A seperated printed report in plain english lets the customer know whats needed and at the end of the day thats what the ESC is all about
DM
 
Hi Devlin,

Yes I agree that plain english is the best and the codes used as you rightly say are always open to interpretation.

Personally I always carefully explain so the customer fully understands and has the option what to do next.

Best wishes,

Rex
 
The original list looks to me like a 16th edition list anyway.

But I would pick up on one
"CPC used as a live conductor (sometimes found in C/H systems and 2 way lighting)"
if the cpc is sleeved as live (ie brown sleve) and their is an alternative cpc or the equipment is class II then what is the problem. I am thinking particularly of boiler installations where two three core cables are used instead of a single 5 core, and a sleeved cpc is used as a switch live.
 
Last edited:
CPC in TW&E should never be used as a Live conductor as then there is NO CPC and if cut in the middle then there is no sleeving

If you mean on flex to things like PIRs and Boiler stats ect thats not as bad as cpc is insulated throughout but its still Shoddy work
 
I went to the IET presentation yesterday about the first amendment. Brace yourselves for the new 'Condition Report' to replace the PIR. It has its own Schedule of Inspections / Tests which look much more detailed, but they've ditched the Code 4 'does not comply but don't worry'. Google 'IET wiring regulations 2008 amendment' to have a look at the draft which includes other stuff like the new special location. Get ready with your sterilised meter probes!
 
Hi RexT

Code 2
19. Anyone circuit has an insulation resistance of less than 20 kilo ohms?
I take it this is a typo?
230/20,000 = 11.5mA
I think I'd call it a code 1 and disconnect it.
Or are we talking about Neutral to Earth?

I tend to agree with Devlin
 
Hi Semaphore,

Thanks, Yes possibly, I think I got the info from the NICEIC inspection and testing book which is very good for getting to grips with testing.
Though I think that the main point is that it has to have sufficent resistance and I guess that has always to be in keeping with the regulations BS7671.
Thanks again,

Best wishes

Rex
 
some of them seem very odd, but would recamend the niceic book on domestic periodic inspection testing and reporting (updated to 17th edition) very good on codes infact spot on
 
If you undertake a PIR in a domestic property and identify a shower circuit does not have a 30mA RCD on it but is cross bonded what code would you give this?
 
Your oppinion on coding these please.. (16th ed Split load CU)

Grid plate in kitchen, Has "washing machine" & "Boiler" behind the grid plate is 2 different circuits, The washing machine is on the RFC, and is RCD protected, also behind the grid id the boiler circuit which is not RCD protected (On main switch side).. Is this worthy of a code?

In the kitchen is a FCU with the label "Cooker" on it, The feed into this is off the RFC, the load side out is in 1.0mm but can not trace where it is going too... Code 3 ????

Above the cooker up high level in the kitchen is a single blank plate, Behind is a 1.0mm t&e in a connector block, Although every circuit is on and switches in the kitchen switched on i cant seem to liven this t&e at all.. Worthy of a code..?

Also on the outside wall is a extractor fan grill, but in the kitchen opposite the grill is no fan! if you tap the wall it feels hollow, as if there was a fan but has now been boarded over.. But surely there will have been a feed there at some point for a fan... But can see any isolator in the kitchen for any type of extractor fan.. Is this worth mentioning on the report?


Last one...

There was an old garage feed that has now been dissconected out of the CU, no MCB, no label, No signs of there ever being a feed for a detached garage.
but there is an SWA on the outside of the house with the lid off the IP box with conductors showing at one end, and on the garage there is the other end of SWA terminated in an IP box with the lid on but it is not fixed correctly to the wall... Is this worth mentioning or if a cable is dissconnected at both ends and not in service do you just ignore it?

Some of these maybe simple to some of you, I dont pretend to know it all and im always learning, especially when it comes to PIR coding.. I will be getting more and more periodics to do so i want to be sure on my coding and i know this is the place to come for advice...
 
The PDF that Steve has sourced is the ESC version 2a - and is the same version as on their website. It blabbers on about sockets likely to be powering outdoor equipment. I wish the ESC ( or a another ) would issue a more recent version that addresses the issues TODAY. For Example is the lack of an RCD on the lighting circuit a Code 1 , Code 2 , Code 3 or Code 4. Please help ...
 
The PDF that Steve has sourced is the ESC version 2a - and is the same version as on their website. It blabbers on about sockets likely to be powering outdoor equipment. I wish the ESC ( or a another ) would issue a more recent version that addresses the issues TODAY. For Example is the lack of an RCD on the lighting circuit a Code 1 , Code 2 , Code 3 or Code 4. Please help ...
 
The PDF that Steve has sourced is the ESC version 2a - and is the same version as on their website. It blabbers on about sockets likely to be powering outdoor equipment. I wish the ESC ( or a another ) would issue a more recent version that addresses the issues TODAY. For Example is the lack of an RCD on the lighting circuit a Code 1 , Code 2 , Code 3 or Code 4. Please help ...


You as someone who carries out PI reporting, need to think about why you think a 'lighting circuit' needs or doesn't need RCD protection. what is it about the circuit that you think needs or doesn't need RCD protection, what regs (if any) are involved etc.
 
That's why I'm asking the question - It is not my opinion that counts - it is the Regs opinion - I can have a personal opinion but when that opinion has a huge financial impact - it is not appropriate to have a personal opinion - the opinion has to be a universal opinion - hence my addition to this thread.

So your comment about questioning my knowledge is not appropriate - I just need a little guidance as to what others consider appropriate Codes for Lighting circuits without RCD protection. Maybe the penny hasn't dropped with me - but it is obviously a Code 4 issue, but was just wondering whether it should be any higher.
 
I wasn't questioning your knowledge, just trying to stimulate thoughts about why a particular circuit may or may not need additional protection via an RCD. All PIR's are one persons personal interpretation of the regs, 2 people would not produce the same report on the same installation.
 
That's why I'm asking the question - It is not my opinion that counts - it is the Regs opinion - I can have a personal opinion but when that opinion has a huge financial impact - it is not appropriate to have a personal opinion - the opinion has to be a universal opinion - hence my addition to this thread.

So your comment about questioning my knowledge is not appropriate - I just need a little guidance as to what others consider appropriate Codes for Lighting circuits without RCD protection. Maybe the penny hasn't dropped with me - but it is obviously a Code 4 issue, but was just wondering whether it should be any higher.

A lighting circuit may need RCD protection if it is part of a TT system,has cables buried at <50mm...or is in a special location.....the code applicable would depend on which of those requirements was not met....there are plenty of lighting circuits which do not require any RCD protection....so I cant see how such a general question can be relevant.
 
Thanks WirePuller - You say that 'plenty of lighting circuits do not require RCD protection' - I think the opposite - I can't think of many older installations that would meet the criteria of not requiring an RCD. Plently unearthed conduiting or cables plastered straight into the walls less than 50mm. Therefore most would require an RCD ie Code 2. Hence my original post ...
 
There can never be a definitive code for a given scenario as the scenario's are infinite, you use your judgement as a competent person, a mini risk assessment if you like and then you apply a code.
 
Though there are some circumstances that can be grey areas and require personal judgement, most are obvious ie. code 4 = not to current regs but poses no danger.

So to me a lighting circuit with cables in wall = code 4


There is a guidance leaflet out, I think its ESC which gives plenty of examples.
 
Thanks WirePuller - You say that 'plenty of lighting circuits do not require RCD protection' - I think the opposite - I can't think of many older installations that would meet the criteria of not requiring an RCD. Plently unearthed conduiting or cables plastered straight into the walls less than 50mm. Therefore most would require an RCD ie Code 2. Hence my original post ...

The regs are not rectrospective,if an install complied with the regs when it was installed,but does not meet the current requirements of bs 7671,in most cases the code would be 4.
A lighting circuit in a commercial property surface wired and on a TN system would not require RCD protection.
A lighting circuit in a domestic property surface wired would not require RCD protection.If that circuit included a bath/shower room,that would be a code 4.
A lighting circuit with buried cables wired prior to the 17th edition (2008)did not require RCD protection,it was safe then and it's safe now...therefore code 4.
RCD protection cannot be a substitute for lack of adequate earthing....if a lighting system with class 1 fittings does not incorporate an earth that would be a code 2 or even a code 1 if there was evidence of a low IR or failing insulation....Lack of RCD to such a circuit ( even if it is required) is a different issue altogether.
 
Last edited by a moderator:

Reply to PIR codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
449
Morning All Qualified electrician, usually stay away from alarms but my friends parents have issues. Texacom Vertas panel, not worked for over 3...
Replies
2
Views
1K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
704
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
829
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock