Good old amendment 3 and the demise of all that's plastic, we have seen many discussions on the good old plastic consumer units, so now for those EICR's where plastic has and will be around for quite some time, SO !!
We all seem to have slightly differing views on this, but here goes.
C2 if there are signs of thermal damage ( I think we would all agree with that one)
C3 dependant on certain locations ie only route of escape or under a staircase.
Other than that no code ?? with just an observation ?? Or no code with no comment at all ??
Throwing a spanner into the works, I code 3 ALL plastic consumer units, but why !!
Of course I could just say its my signature and my decision, plus a C3 is not failing the install, but there's another reason.
Before saying, I would be interested to see what your thoughts are, as I think this could prove quite interesting.
 
I tend to make a note of the type and layout of the consumer unit in the general comments box. i.e split load Hager plastic CU.

I only code when I feel it is warranted, not as a default.
 
C3 by default is understandable (afterall the code is defined as Improvement Recommended); if nothing else it's arse-covering and doesn't fail the EICR; Much like any other nonconformities to current 18th edition; C3 so it's on record in more than just a 'passing comment' and is inkeeping with the purpose of the C3 code - obviously go further attaching relevant regs from 7681, EAWR and that like where appropriate to further explain your engineering judgement.

I find it interesting that we focus on CUs being non-plastic and yet permit things like REC2 Isolators (with or without SPD) and Thier assemblies to be plastic, along with adaptable boxes, for that main being plastic - I believe 5839 makes an stipulation that any junction boxes et all are to be metalic to ensure system integrity bit would have to find out the relevant clauses to confirm.
 
I wonder how long it will be before this goes even further and we have metal MCB's, RCD's, RCBO's and main switch's, even to the extent of T&E being metal sheathed, or maybe back to metal conduit becoming compulsory.
 
I wonder how long it will be before this goes even further and we have metal MCB's, RCD's, RCBO's and main switch's, even to the extent of T&E being metal sheathed, or maybe back to metal conduit becoming compulsory.
What about lead sheathed cables ? Mad idea, but it might work...
 
Thanks for the replies, as said we all have our reasons for coding these things or not coding as we feel fit.
For what its worth, I like most have seen these reports gain page after page as times gone on. In particular the Inspection schedule has become very comprehensive.
So looking at section 4 and in particular 4.4
I feel where plastic CUs are concerned, we have little choice but to C3 as an absolute minimum. If Regulation 421.1.201 isn't met. ie condition of enclosure in terms of fire rating. Then I will be covering my proverbial. Sometimes I see these schedules as trick question scenarios.
So default Code 3 thankyou IMHO.
As said cover your arse, its your signature.
 
So looking at section 4 and in particular 4.4
I feel where plastic CUs are concerned, we have little choice but to C3 as an absolute minimum. If Regulation 421.1.201 isn't met. ie condition of enclosure in terms of fire rating. Then I will be covering my proverbial. Sometimes I see these schedules as trick question scenarios.
So default Code 3 thankyou IMHO.
As said cover your arse, its your signature.
The condition in terms of fire rating of which "enclosure" are you referring to?
Since January 2016 Amendment No. 3 to BS 7671 (421.1.201)IET Wiring Regulations states that within domestic (household) premises, consumer units and similar switchgear assemblies shall have their enclosures manufactured from non combustible material, or be enclosed in a cabinet or enclosure constructed of non combustible material and comply with product standard BS EN 61439-3.
Not quite sure where a properly fire lined cupboard under the stairs works with BS EN 61439-3
 
As per the eicrs section 4 of the schedules 4.4 the consumer units enclosure itself. Granted if its in a non combustible enclosure then the relevant reg would be satisfied and compliant. But most pre AMD 3 consumer units are simply mounted as installed as indeed they would be. But under those conditions the schedule ie 4.4 leaves you with little choice but to give it some code ie 3. As a plastic c/u by definition is not constructed of non combustible material. IMHO.
 
Thanks for the replies, as said we all have our reasons for coding these things or not coding as we feel fit.
For what its worth, I like most have seen these reports gain page after page as times gone on. In particular the Inspection schedule has become very comprehensive.
So looking at section 4 and in particular 4.4
I feel where plastic CUs are concerned, we have little choice but to C3 as an absolute minimum. If Regulation 421.1.201 isn't met. ie condition of enclosure in terms of fire rating. Then I will be covering my proverbial. Sometimes I see these schedules as trick question scenarios.
So default Code 3 thankyou IMHO.
As said cover your arse, its your signature.
So C3 absolutely as it doesn't 100% comply with 421.1.201 - I understand

So I assume C3 - no question if the installation doesn't comply with 514.4.1 or 514.4.5 as well?

(Cables not coloured blue; brown, black, grey, blue)


Surely if we decide that anything not 100% compliant with the latest standard must be C3 as a minimum, this applies across the board, not just specific areas such as cu's
 
So C3 absolutely as it doesn't 100% comply with 421.1.201 - I understand

So I assume C3 - no question if the installation doesn't comply with 514.4.1 or 514.4.5 as well?

(Cables not coloured blue; brown, black, grey, blue)


Surely if we decide that anything not 100% compliant with the latest standard must be C3 as a minimum, this applies across the board, not just specific areas such as cu's
Its the implications as per the schedule and specifically section 4s 4.4 that leaves you with limited options. Its not about retrospective installations. Ie installs that complied with older versions of BS 7671, not necessarily having to comply with latest versions. Its more specific than that. Its about how you respond and classify to that particular section on consumer units and there enclosures. As said I cant see that the way the eicr phrases that particular section gives you much by way of options. I like most have read it many times, and still come to a C3 conclusion in most instances. But then, thats my view, but always interesting to discuss other viewpoints on this. As said we all need to cover ourselves when signing these things.
 
Its the implications as per the schedule and specifically section 4s 4.4 that leaves you with limited options. Its not about retrospective installations. Ie installs that complied with older versions of BS 7671, not necessarily having to comply with latest versions. Its more specific than that. Its about how you respond and classify to that particular section on consumer units and there enclosures. As said I cant see that the way the eicr phrases that particular section gives you much by way of options. I like most have read it many times, and still come to a C3 conclusion in most instances. But then, thats my view, but always interesting to discuss other viewpoints on this. As said we all need to cover ourselves when signing these things.

Why does it leave you with limited options? 5.1 would leave you with the same options for identification of conductors.

Compliance (or not) with any previous standards does not form part of periodic inspections, the question is: is the installation satisfactory or unsatisfactory? (~ reasonably safe vs unsafe) - the same non-compliance such as premature wiring collapse - it may have been compliant with a previous standard (which is irrelevant) may generate C2, C3, or nothing, - if the cable is unsupported such that failure could cause entrapment - C2 ; if the failure wouldn't case any issue then depending upon the severity it may be C3, or perhaps just an honourable mention.

I see no difference in any other aspect, the plastic cu may be C2, C3, or mention; cable identification perhaps C3 or mention, or nothing at all, cable supports, etc etc.
 
Why does it leave you with limited options? 5.1 would leave you with the same options for identification of conductors.

Compliance (or not) with any previous standards does not form part of periodic inspections, the question is: is the installation satisfactory or unsatisfactory? (~ reasonably safe vs unsafe) - the same non-compliance such as premature wiring collapse - it may have been compliant with a previous standard (which is irrelevant) may generate C2, C3, or nothing, - if the cable is unsupported such that failure could cause entrapment - C2 ; if the failure wouldn't case any issue then depending upon the severity it may be C3, or perhaps just an honourable mention.

I see no difference in any other aspect, the plastic cu may be C2, C3, or mention; cable identification perhaps C3 or mention, or nothing at all, cable supports, etc etc.
We differ in our opinions on this one. I cant see how red and black vs brown and blue can be compared to a consumer unit by virtue of its build material having the ability to contain a fire. So I wouldn't lose any sleep over 5.1. Or not coding it as long as conductors have been correctly connected and identified. And if an electrician has to be warned by a label that an installation contains wiring to 2 versions of BS 7671, then I would question there competence.
Its all about the hows and whys of personal judgements. But I just feel that sometimes, the way these things are written leaves a lot of grey areas.
 
New posts

Reply to Plastic consumer units and how to code them in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
900
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
645
Hello engineers. I did EICR in two bed rented flat in a block of flats. There is old plastic fuseboard just above the entry door. There are only...
Replies
19
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock