Discuss Plug in 2kw heater in shed Will it go kaboom??! in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
4
I use my shed for pottery and it’s currently wired to have 2 sockets and a light switch (fused down from one of the sockets). Currently I draw less than 300 watts of power. As it’s getting cold I’d like to plug in a heater out there but my husband says it’s not a good idea as my shed isn’t wired up for that, (he might just be being tight) and he’s definitely no electrician, so
I’ve come here looking for guidance!!!

From the information on our consumer unit and a bit of investigation I know it is wired on a 20Amp Rcbo with 2.5mm T&E clipped to the joists under the floor of the house it then exits the house to an outdoor socket and then from there, there is a run of 2.5mm SWA to my pottery shed. That terminates inside the shed to a junction box and the sockets are fed from there. There’s approx 20m of internal wiring plus 20m of outdoor SWA. Is it safe to plug in my 2kw heater please?
 
  • Like
Reactions: DPG
No it will be fine. The light may 'dip' a bit when the heater is turned on but nothing to worry about.
 
Full marks to the OP for asking a good question and giving all relevant details!
Awww thanks I did search the forums first to see if a similar question had already been asked (worryingly it seems there’s quite alot of people running power to sheds with absolutely no clue) so I had a heads up first of what info was required. Just glad to have the reassurance that Im not going to nuke myself!
 

Reply to Plug in 2kw heater in shed Will it go kaboom??! in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hey, I have a shed in my garden that was built and wired up by my granddad a lonnng time ago and it currently uses 2 core/twin and earth cable...
Replies
2
Views
811
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
541
I have a sub panel about 75ft from my house attached to my shed that feeds a pool pump, some outlets and a pool heater which is no longer used...
Replies
0
Views
545
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock