Hello all,

Have been doing some work in a large building complex, the original building has a TNS supply but the large extension to the building has a seperate PME supply.

At present there are no main protective bonding conductors to water/gas/oil and these services are common to both old and new parts of the building. If these MPB conductors are taken to one of the origins (PME for example) I'm imagining that will cause issues by mixing two Earth potentials (PME potential on pipe work and TNS potential from cpc's). Have been looking through the BGB but can't find an answer to my question. Any ideas?
 
Re: TNCS & TNS supply in same building

IMO, if the extraneous parts are common to both areas, then you must combine the earthing arrangements . you don't want a pd between the 2 earthing systems. you could dis. the TN-S and connect the whole system to the PME.
 
Re: TNCS & TNS supply in same building

When new supply applied for, did the DNO know that it was to remain as one building? Is having 2 supplies in one building OK? 2 x points of isolation.
 
Re: TNCS & TNS supply in same building

The fun and games will start if the two supplies are on different feeders/transformers. It could cause quite bad circulating currents. Have a word with the DNO.
 
Re: TNCS & TNS supply in same building

Whats that Tel? Dis. The TNS??? The mother, the king, the queen of all earthing???? :laugh:
 
Re: TNCS & TNS supply in same building

When new supply applied for, did the DNO know that it was to remain as one building? Is having 2 supplies in one building OK? 2 x points of isolation.

I don't know when the extension was built, but I believe that this is a question that surely should've been raised at the time.

The fun and games will start if the two supplies are on different feeders/transformers. It could cause quite bad circulating currents. Have a word with the DNO.

There is a substation on site, coincidentally the SSE where there on Wednesday with temporary backup generators as they were shutting down the onsite substation for ongoing works in a neighbouring village. I'm pretty sure that both supplies are coming from there.

Either way, I agree that they need to be contacted.
 
Re: TNCS & TNS supply in same building

I don't know when the extension was built, but I believe that this is a question that surely should've been raised at the time.



There is a substation on site, coincidentally the SSE where there on Wednesday with temporary backup generators as they were shutting down the onsite substation for ongoing works in a neighbouring village. I'm pretty sure that both supplies are coming from there.

Either way, I agree that they need to be contacted.

If it’s a transformer dedicated to what I assume is an industrial estate, I’m surprised it’s a mix of TN-C-S and PME. That said they could be on separate feeders from the transformer feeder pillar installed at different dates.

What is the rating of these supplies?

Before you do anything talk to the DNO. You’ve decided that anyway.
 
Re: TNCS & TNS supply in same building

IMO, if the extraneous parts are common to both areas, then you must combine the earthing arrangements . you don't want a pd between the 2 earthing systems. you could dis. the TN-S and connect the whole system to the PME.

I’m surprised at you for suggesting that Tel.
 
Re: TNCS & TNS supply in same building

So you have a PME supply & a TN-S supply in the same building?
Do the DNO know about this?
Or, have there been building changes since the supplies were installed?
 

Reply to PME & TNS supply in same building in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
The other night, neighbour knocked my door. She said she'd gone to use their outdoor tap, and she thought she'd got a shock. Went and had a look...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock