Discuss Position of socket for integrated oven in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
6
Hi, I am looking to install an integrated oven, however it's position would mean the socket on the wall will be directly behind it. Is this allowed? is this safe? I just worry it could be too hot there.

I could move the socket, probably nearer the floor so it's below the oven. If I do this would it have to be above 45cm?

Thanks for reading
 
Put it in an adjacent kitchen unit where it will be accessible. Bad idea to have it behind the oven!
 
Place it wherever it is most accessible and practical.

If you can't immediately access the socket it is also advisable to feed it through a double pole switch so it can easily be isolated if faulty or just for maintenance such as cleaning.
 
Is it not possible to move the socket into one of the adjacent base units and make a small hole to feed the plug top through
 

Reply to Position of socket for integrated oven in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
705
Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how my oven is currently wired up, followed by 3...
Replies
0
Views
942
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
724
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock