Discuss Post Smart Meter Main Breaker Tripping Intermittently in the UK Electrical Forum area at ElectriciansForums.net

If the Wylex is only for the Storage Heaters wouldn't it only need the night tariff and the MEM 2000 should have both tariffs?

Edit: Had a look, there's an upstairs heater on the Memara 2000 but that's usually not used. Otherwise Up Sockets, Down Sockets, Up Lights, Down Lights.

The day wire being slightly loose was my pet theory. Anything else seems complicated and certain to lead to replacing a lot of the equipment without being certain of a resolution.

Even replacing the whole CU doesn't seem to offer any guarantees without reasonable certainty of what the problem is.
 
Last edited:
If the Wylex is only for the Storage Heaters wouldn't it only need the night tariff and the MEM 2000 should have both tariffs?
The right hand side of the Wylex has a B6 breaker, so likely lighting. This CU would therefore need both supplies.
Can you confirm there are no RCD's in the Wylex board, a photo with the flap up would show this. You could also remove the sticker that should have been removed years ago during installation!
The day wire being slightly loose was my pet theory.
Yes, it might be a loose connection but my money is on the Mem 2000 CU being affected by interference. The odds are stacked in favour of this - we've known this exact scenario before, and the RCD wasn't tripping before the smart meter was installed.

As I see it there are the following options:
1 - Try turning all the MEM 2000's breakers off leaving the RCD on. Sit in the dark for a while. If RCD still trips it strongly suggests the meter is causing it. It isn't 100% conclusive as it could technically also be a Neutral-Earth fault but you weren't seeing a fault before the meter arrived.
2 - Get a sparks to check connections
3 - See if a sparks can economically replace the RCD with an isolator and separately power the RCD with no load to 100% prove the point. Spares for the MEM2000 board are only available 2nd hand now, so this might be more trouble that it's worth.
4 - Reluctantly accept that the MEM2000 board was great in it's day but a replacement would highly likely solve the problem. It's only 4 easy circuits, a replacement won't be expensive or difficult. If you went for an RCBO board then each circuit has separate RCD protection, making this kind of scenario much easier to diagnose. You'd also then have type A RCD protection which copes much better with modern loads. (The MEM2000 has type AC which is effectively banned in latest regs for new installs)
5 - Try and get OVO to remove the smart meter. You could try pointing out this thread on their own forum:

 
The right hand side of the Wylex has a B6 breaker, so likely lighting. This CU would therefore need both supplies.
Can you confirm there are no RCD's in the Wylex board, a photo with the flap up would show this. You could also remove the sticker that should have been removed years ago during installation!

Yes, it might be a loose connection but my money is on the Mem 2000 CU being affected by interference. The odds are stacked in favour of this - we've known this exact scenario before, and the RCD wasn't tripping before the smart meter was installed.

As I see it there are the following options:
1 - Try turning all the MEM 2000's breakers off leaving the RCD on. Sit in the dark for a while. If RCD still trips it strongly suggests the meter is causing it. It isn't 100% conclusive as it could technically also be a Neutral-Earth fault but you weren't seeing a fault before the meter arrived.
2 - Get a sparks to check connections
3 - See if a sparks can economically replace the RCD with an isolator and separately power the RCD with no load to 100% prove the point. Spares for the MEM2000 board are only available 2nd hand now, so this might be more trouble that it's worth.
4 - Reluctantly accept that the MEM2000 board was great in it's day but a replacement would highly likely solve the problem. It's only 4 easy circuits, a replacement won't be expensive or difficult. If you went for an RCBO board then each circuit has separate RCD protection, making this kind of scenario much easier to diagnose. You'd also then have type A RCD protection which copes much better with modern loads. (The MEM2000 has type AC which is effectively banned in latest regs for new installs)
5 - Try and get OVO to remove the smart meter. You could try pointing out this thread on their own forum:


Sorry for the somewhat slow response.

It wouldn't be possible to test that way since when I say intermittent it's not daily but closer to 2 or 3 times a week.
 

Attachments

  • 20220404_030436.jpg
    267.4 KB · Views: 36
It wouldn't be possible to test that way since when I say intermittent it's not daily but closer to 2 or 3 times a week.
I think most reports of smart meters tripping RCD's were a little bit more frequent than that, often every 24 hours.

Time to find/call a sparks who will very quickly be able to see how close the RCD is to tripping 'normally' and if high track down why.
If this leads nowhere, then there are a couple of Memera2000 main switch isolators on ebay at the moment for under a fiver. You could suggest a sparks temporarily replaces the RCD with one and powers the RCD separately as this would prove the point if it's the meter doing it.
 
I think most reports of smart meters tripping RCD's were a little bit more frequent than that, often every 24 hours.

Time to find/call a sparks who will very quickly be able to see how close the RCD is to tripping 'normally' and if high track down why.
If this leads nowhere, then there are a couple of Memera2000 main switch isolators on ebay at the moment for under a fiver. You could suggest a sparks temporarily replaces the RCD with one and powers the RCD separately as this would prove the point if it's the meter doing it.
Had OVO/SSE engineer attend today. He intended to replace the smart meter with 2nd generation as he was going through the commission process the Garage breaker tripped and wouldn't reset. Nothing on in garage or plugged in. He explained there are several types of breakers that the 2nd generation nuisance trips cause by the radio waves. Proteus boards being one type. He said he would re-install the original after 'the fix' tin foil didn't work. End result I no longer have smart meter connectivity because the original was no longer connected to DCC. Waiting to hear from OVO again.
 
Had OVO/SSE engineer attend today. He intended to replace the smart meter with 2nd generation as he was going through the commission process the Garage breaker tripped and wouldn't reset. Nothing on in garage or plugged in. He explained there are several types of breakers that the 2nd generation nuisance trips cause by the radio waves. Proteus boards being one type. He said he would re-install the original after 'the fix' tin foil didn't work. End result I no longer have smart meter connectivity because the original was no longer connected to DCC. Waiting to hear from OVO again.
Which board is the garage breaker on? Or is that on a board that hasn't been photographed yet?

I'm trying to decide if there was a genuine problem with his new meter and a Proteus device, or he somehow mixed up the tails and that was the cause of an RCD objecting.

As 7 months have now passed it might be worth considering getting the whole install tidied up from the meter tails onwards and a new modern consumer unit fitted.
This smart meter radio interference thing only affects older consumer units and devices in my experience. I've not known it happen with anything fitted in the last 5-10 years.
 
Which board is the garage breaker on? Or is that on a board that hasn't been photographed yet?

I'm trying to decide if there was a genuine problem with his new meter and a Proteus device, or he somehow mixed up the tails and that was the cause of an RCD objecting.

As 7 months have now passed it might be worth considering getting the whole install tidied up from the meter tails onwards and a new modern consumer unit fitted.
This smart meter radio interference thing only affects older consumer units and devices in my experience. I've not known it happen with anything fitted in the last 5-10 years.
My post is not about the original case, it was my experience yesterday. Prior to the second generation install the generation 1 meter had no issues. According to the engineer it was a radio wave issue identified as affecting certain types of RCD. As for the board, it was just one consumer unit. The garage breaker is an RCCB that has had no previous issues. Seems once again the second generation we were promised was the solutions to drop outs etc isn't. Now there is a third type supposedly available next year. Meanwhile our smart meter is no longer connected to DCC
 

Reply to Post Smart Meter Main Breaker Tripping Intermittently in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
438
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
605
Hello, I am on Economy 7 and I have storage heaters and a hot water tank connected to a separate CU for my off-peak usage. The timer that switches...
Replies
3
Views
2K
Charah
C
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
921
Hi All, I have a 1950s rental house with a 100 amp main panel with a main shut off breaker. Breakers are Eaton/Cutler Hammer type, so the...
Replies
2
Views
979

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock