Hi All,

First of all apologies for the potentially novice sounding question believe it or not I’ve been a qualified electrician for 10 years but I’ve always worked cards in so calculations have not been something I’ve ever considered I just install the sizes on the spec however I now have to design a small upgrade so looking for clarity on something.

I am installing a 3 phase sub mains to a 24 single or 8 3 phase ways board.

The load on the 3 phase DB is going to be entirely single phase and although balance is going to be as close as possible it will not be perfectly balanced.

I have a total of 38kw of load which will be split 14-12-12 across L1-L3.

Total load is 165A or thereabouts so the question is does the 3 phase cable current carrying capacity refer to the total load (165) or the per phase (approx 55)

Also with that in mind is the 3 phase load then considered 165A or is it 52A applying the calculation to 38kw?

For this I’m not taking into account volt drop or anything I have an app do actually do the calculations but I want to understand how it works.

Thanks in advance
 
TL;DR
Does the current carrying capacity of 4 core cable refer to overall or per phase when feeding single phase loads.
Last edited:
55A

Although this doesn't account for power factor , nor unbalance

So depends on the type of load, and diversity of course.
Thanks, do you know the calculation behind this though? So if I put the calculation into any cable calc online when I state that the overall load is 165A it wants a 70mm cable but if I put 55 which would be the per phase it comes down to 16mm im trying to understand why it’s 55 not just outright the answer
 
I would think it would be the load per phase you enter into the calculator, or more correctly the highest of the three.

I would generally consider the possibility of future expansion too.
 
think of 10 circuits at 10A each
single phase easy,
L= 100A
N= 100A

split them across 3 phases and you have

L1 4 x 10A =40A
L2 3 x 10A =30A
L3 3 x 10A =30A
N = 10A

in simple terms.
 
Formally

I = P/(3 × Vph) (phase - neutral voltage)

so 38000/(3 x 230) = 55A

I = P/(sqrt3 x V[ph-ph]) (phase - phase voltage)

So 38000/(1.73 × 400) = 55A


Ideally though add up each current that you apply per phase, as stated above, basically if you have 4 10A loads then you would have one phase with 20A whilst the others have just 10A, so you would size for more than 20A

If you just calculated it by power 10A x 230V x 4 = 9.2kW

The calculation would be 9200/(3 × 230) = 13.3A

Which is an average, and not the actual expected current (too low on one phase)
 
Thanks for the answers.

So essentially although the total load is the 165 on the cable calcs the cable sizing is based on a single phase load so given than my largest load will be 61A on L1 use a 16mm 4 core to allow for future expansion?

That way I can then utilise 100A per core if required?

Thanks for that though really helpful
 

Reply to Power calculations help please? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
1
Views
358
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
316
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock