- Reaction score
- 8,777
Regarding 3 phase IR tests for initial verification, I'm wondering how people actually do it efficiently.
GN3 says to IR test between all phase permutations, then:
L1+L2+L3 connected together to N
L1+L2+L3 connected together to E
N to E
The OSG further comments that if the group test to earth is low then do each conductor individually to earth to find where the issue is.
So, two questions:
1) If anyone does it this way, how do you go about quickly joining the lives together, or have people made up special test leads with three probes/leads stacked for the purpose?
2) Isn't it just as valid, quicker, and simpler to IR test each phase to N and each phase to E instead of messing about joining them up? Anyone do this?
GN3 says to IR test between all phase permutations, then:
L1+L2+L3 connected together to N
L1+L2+L3 connected together to E
N to E
The OSG further comments that if the group test to earth is low then do each conductor individually to earth to find where the issue is.
So, two questions:
1) If anyone does it this way, how do you go about quickly joining the lives together, or have people made up special test leads with three probes/leads stacked for the purpose?
2) Isn't it just as valid, quicker, and simpler to IR test each phase to N and each phase to E instead of messing about joining them up? Anyone do this?