see his view when I asked the question today was this

You're requested to replace a consumer unit. In an operational domestic property, to improve safety.

You're not getting paid to come in and do an eicr first.
You are there to do the board change and then provide an eicr to state the reason for producing report as "Due to CCU being updated to current standard."
List any limitations. Which there may be in an existing property, and code any issues. Do all your dead tests and live tests. And at the same time your visual inspection. Broken screw on a socket, cracked faceplate, insufficient csa of a services earth. Code them. Then if the client wishes to have the remedial work carried out then you do an MWC, but you should redo the report as well to show it clear for whatever purpose it has been requested. Generally insurance companies.

He stated numerous times throughout the course today, you can only recommend you can't enforce. If you believe something is seriously dangerous you can only try and implore the client & report it to the HSE if they ignore your advice.

Also an EICR is not as important as an EIC, and that an EIC is for new installations or new circuits, and that you are inferring that they meet all BS7671 current standards of installation and have been inspected at all steps of the installation. Which you can't guarantee in a consumer unit change as you're only seeing connections to the equipment in the installation.
Also you should have no limitations in a new install. Which there can be in an existing building.

There's zero places on an EIC to mention any limitations, which is 1 of the reasons his explanation made sense. Along with the fact you can't state installation method meets BS7671 if you couldn't inspect it along the way.

And without damaging the fabric of the installation or removing kitchen units or appliances which can be on many limitations you cannot prove they do.
You can only report on the condition of the installation based on test results on the day and a visual inspection and code any issues if there are any.

I'm lost now lol as his explanation did make sense if you can follow my poor description of what he said.

But basically he said as you are not altering any circuits in the installation it wasn't an EIC, and that effectively a CCU was equipment but as it was such a major piece of equipment was not suitable for a MWC, and therefore you do an EICR.
 
Last edited:
see his view when I asked the question today was this

You're requested to replace a consumer unit. In an operational domestic property, to improve safety.

You're not getting paid to come in and do an eicr first.
You do the board change and an eicr to state the reason for producing report as "Due to CCU being updated to current standard."
List any limitations. Which there may be in an existing property, and code any issues. Do all your dead tests and live tests. And at the same time your visual inspection. Broken screw on a socket, cracked faceplate, insufficient csa of a services earth. Code them. Then if the client wishes to have the remedial work carried out then you do an MWC, but you should redo the report as well to show it clear for whatever purpose it has been requested. Generally insurance companies.

He stated numerous times throughout the course today, you can only recommend you can't enforce. If you believe something is seriously dangerous you can only try and implore the client & report it to the HSE if they ignore your advice.

Also an EICR is not as important as an EIC, and that an EIC is for new installations or new circuits, and that you are inferring that they meet all BS7671 current standards of installation and have been inspected at all steps of the installation. Which you can't guarantee in a consumer unit change as you're only seeing connections to the equipment in the installation.
Also you should have no limitations in a new install. Which there can be in an existing building.

There's zero places on an EIC to mention any limitations, which is 1 of the reasons his explanation made sense. Along with the fact you can't state installation method meets BS7671 if you couldn't inspect it along the way.

And without damaging the fabric of the installation or removing kitchen units or appliances which can be on many limitations you cannot prove they do.
You can only report on the condition of the installation based on test results on the day and a visual inspection and code any issues if there are any.

I'm lost now lol as his explanation did make sense if you can follow my poor description of what he said.
 
But hey. I'm only getting into this as I'm now working on my own and want to do it right. Hence doing the initial verification course and now the periodic. So am open for any advice. Hence why I checked with the tutor today and will have him double check.

As I will be using the reasons given here to do so lol
 
OK, didn't realise we were talking about the replacement of a DB. I thought you were referring to remedial works to an installation.

For the replacement of a DB you must issue an EIC. This certificate in no way relates to the existing installation (except for the comments on existing installation section). Your EIC solely relates to the replacement of the DB. You are verifying that ADS will operate for the circuits you are connecting (to ensure that your DB installation is safe) but you are not certifying the existing installation. You won't be verifying cables being installed in prescribed zones, etc. unless you have installed any cables. So this would be N/A. Your schedule of inspections is again only relating to your installation of the DB as confirmed by your extent of works section.
 
Thanks for that Risteard, I assume that's how niceic require it to be done?

Though I was thinking of doing stroma if I do join a CPS but will decide later in the year or during 2018 what way to go.
 
What would Stroma do for you in Northern Ireland? Napit used to be required for B&Q Kitchen's, but pretty sure that's NICEIC now. AFAIK Ikea also requires NICEIC.

NICEIC Approved Contractor is the main one, it'll allow you to undertake work for Councils and the Housing Executive.

There is ECA and JIB but this are for bigger firms than one man bands.
 
So are there actually any benefits from being in Niceic?

Is there actually any benefits for being in a cps in NI? Apart from being eligible to do that stuff mentioned above if in the niceic?
 
Any of the part p crowd like Stroma, Napit etc etc is of no use at all.

The only one I'd consider looking at is NICEIC Approved Contractor. I'm not with them, but in Northern Ireland for a one man band it's either them or none.
If no one is specifying it, and you're not losing any work from not being registered I wouldn't bother.

I lose about 2-3 small extensions a year and the odd entertainment licence (basically an EICR for a Pub)
 
So only need stroma if we end up getting part p then?

Are the extensions and entertainment licence jobs only accepting Niceic?

Is it the same on the mainland? Or do we just get ridden by the niceic monopoly?

Have you been asked to join this SparkSafe thing the ETT are trying to push?
 

Reply to Price check please, NI sparks in particular. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all! Posted on here a couple of years ago and got great advice. Have been self employed a couple of years now and always find pricing work the...
Replies
10
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
202
Good afternoon all, 1st time posting here and id like to ask about pricing to get a general feel of where I fit in the domestic market. I...
Replies
10
Views
3K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K
Hey all, Could do with some help. I had a company recommended to me who quoted me to do an EICR on my rental property. (£265). I thought this...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock