Discuss Problem circuit in the UK Electrical Forum area at ElectriciansForums.net

timhoward

-
Esteemed
Arms
Supporter
Reaction score
8,774
Thought I'd seek some advice on something has been frustrating, and the frustration may now be clouding judgement....!

It was 30A rewirable fuse, 6mm T+E, at unknown point changing to 4mm SWA feeding CU in shed.
At point of CU change I discovered one double socket and a FCU also fed 'somehow' from this circuit.
Since board change it's been disconnected as there have been higher priorities to sort like broken rings and live abandoned cables.
I should add this is all in a house where 'trust nothing' applies, already found taped live cables in walls and loft, and all sort of random DIY-ness. I wanted to have some confidence how this had been done as I didn't really know what I was potentially reconnecting, which on the basis of other things seen could be absolutely anything at all.

My original thinking was that had it been just an FCU on a spur, or just one single socket, that would seem ok as current is limited to 13A on the spur.

After some faffing around with a camera, by some miracle I've found one joint box. It's in a stud wall, but one side is tiled floor to ceiling, then plasterboard on top of that. The other side is tiled from worktop up. The joint box is just above worktop height (of course!). It's a flat roof above. This is another one of those "why make it beautiful and then think about electrics" cases.

By pulling the under-worktop cupboard out and making a discreet hole that will be hidden I can rest now my hand on the joint box and confirm that it has the 6mm T+E in and out, and a 2.5 T+E going to double socket, and 2.5 T+E going from there on to the FCU. So I at least know how it's wired now.

Options seem to be:
1 - make an almighty mess to get access to joint box, remove spur and check connections, and run new radial for socket and FCU.
2 - safely terminate the 2.5 T+E coming out of the joint box in a dry-wall box below worktop and run a new radial into the area for the socket and FCU. The Sub-main could then be connected again.
3 - Possibly omit double socket, and use spur from joint box to feed FCU. My understanding is that this would be permitted.

I've still not found where the T+E becomes SWA but might have to trust that one as long as it all tests out ok.
So main question is what you think of options 2 and 3. Do they seem reasonable?
 
I feel so sorry for this customer. Everything seems to rapidly turn into a mini nightmare and nothing has been done right.
I've not been able to bring myself to point out that the saniflo toilet ejects it's waste in washing machine waste hose - I'm no plumber but fairy sure that 32mm PVC pipe is the usual standard....
 
I feel so sorry for this customer. Everything seems to rapidly turn into a mini nightmare and nothing has been done right.
I've not been able to bring myself to point out that the saniflo toilet ejects it's waste in washing machine waste hose - I'm no plumber but fairy sure that 32mm PVC pipe is the usual standard....
Poo
 
whoever installed that saniflow may be nominated for "wet-pants of the year" award. by defying the laws of physics poosics (sh*t flows downhill) , he could rewrite the plumbers guide to gravity.
 
Sadly there are many residences that have been hacked about over the years, not done to Regs and some dangerously so. I would discuss methods to remedy with Owner as some will see the long term benefit of the full (but messy) job.

Keep looking for the SWA starting point, as it will likely be
1619338656269.png
too :) .
 

Reply to Problem circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
628
I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
Replies
2
Views
808
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
550
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
372

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock