Can you clever people advise as to why I might be having an issue with my ceramic kiln. I am a potter not an electrician so I will endeavour to give you what technical information I have.

11kw kiln running off a domestic board with its own 50A fuse on board in the house, 15m lenght of 10mm cable runs from house into my studio where it has its own board with a 62A breaker and 50A fuse.

The fuse in house is tripping when firing cycle reaches about 1060 degrees (kiln should reach 1250 degrees). It used to reach 1180 degrees before tripping but over a few years it has been tripping earlier and early.

The firing cycle of the kiln goes up slowly, automatically over 5 hrs automatically turning on and off until the end when its on full load. Kiln fired fine with no tripping day before yesterday (post element change) when taken fast at full load to temperature, but when I did a slower firing last night it tripped.

Kiln engineer took a reading of 45Amp and there is a drop in voltage from 240 to 232 when under load.

I have had kiln serviced and elements replaced this week and tripping still happening so pretty certain its not the kiln.

Questions: Can anyone see an issue with the electric maths? Is the cable thick enough? Can a domestic fuse be upped to next level? Can cables get tired and old?

Any advise as to what to try next would be greatly appreciated as I'm soooo frustrated with this ongoing issue.

Cheers lovelies!
 
What sort of ‘fuse’ is it. Is it a circuit breaker MCB, RCD or a combination.

Things ‘trip’ due to earth leakage and over current.

I would have pointed towards the elements leaking as the temp rises but if they are new it’s unlikely.

Keep in mind you will have a control circuit that operates the Kiln so it’s possible to have a faults in that.

Pretty hard to diagnose without being there.
 
Last edited:
Hi Lee. Thanks for replying.

the fuse thats tripping is a B50A circuit breaker 30mA on my domestic board. The 62A RCD is in the studio next to a B50A circuit breaker neither of these trips.
 
So it’s possible it’s an earth fault.

You need to get the Insulation resistance measured on the Kiln. Was this done after the elements were replaced?
 

Reply to Problem with 11KW Kiln in domestic setting in the Electricians Jobs area at ElectriciansForums.net

Similar Threads

Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
2K
Hi, just found this forum! I'm in Australia Maybe people here can suggest what may be causing a power issue I have. Appreciate any suggestions...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock