Discuss Prospective Fault Current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

Graham Coughlan

Two questions here really

Am i right in thinking that PFC is Prospective Fault Current or is it power factor corection?

Second question is why is it important to know the Prospective Fault Current?

Thanks
 
Power factor is normally just PF, i know PFC as Prospective Fault Current.

You need to know the value of PFC on a circuit to confirm the protective device for that circuit could withstand it, without creating damage to the protective device and in turn the device not operating.
 
As said above you need to know the fault current to ensure the kit can withstand the fault.

Hv switchgear as a rule of thumb has to be able to withstand full fault current for 5seconds this gives circuit protection time to operate.
 
PFC is required to determine the size of CPC, whether the CPD will operate within the specified time, and whether the breaking capacity of the CPD is sufficient.
CPC = Circuit Protective Conductor.
CPD = Circuit Protective Device.
 
Last edited by a moderator:
The abbreviation "PFC" could be used for either Prospective Fault Current (PFC) or Power Factor Correction (pfc) it depends on the context in which it's used, the normal convention as I've shown is to use capital letters for the former and lower case letters for the latter to avoid confusion.
 

Reply to Prospective Fault Current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
795
Hi all Was looking in to the adibatic equasion as our company will not let us add on to a Ring circuit with 1mm cpc.. I want to give some...
Replies
12
Views
1K
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
774
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
0
Views
250

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock