Discuss Quantum Heaters Dimplex Wiring supplies in the UK Electrical Forum area at ElectriciansForums.net

catdog

-
Reaction score
13
Hi all,

Just wondering if anyone had fitted many of the quantum heaters with dual supply. Im looking at a job to fit a few and wondered peoples thoughts on spuring off the ring final circuit for the 24 hour supply to the heater (Rated at 1.5kw) via a fused spur? Also does anyone know if there is any mention of how many individual loads you can have on a ring final circuit (32 amps, 2x2.5mm) assuming they don't all add up to more than 32 amps. Can only think about the reg relating to not having a fixed appliance rated more than 3kw I think (assuming relating to ovens/hobs).

Basically was wondering how many quantum heater 24 hour supplies I could link into the ring final circuit and then add additional circuits for the rest of the heaters ( have about 3 or 4 quantum heaters to install)

any advice appreciated.

thanks.
 
Original storage heaters already have their own individual circuits but only have single off peak supply but obvs the quantums require a 24 hour supply too.

And buzzlighyyear I'm offended . Some people would question that too.....
 
I'd personally be loathe to spur the 24 hour supplies off an existing RFC, if each one is 1.5kW you could soon be overloading with other existing bits also on the ring, but subject to length of cable runs, installation method etc you could probably run a 1.5 to each one on a 10a MCB per heater.
 
Yeah that's why I asked, that was my fear of overloading. Think practically prob wouldn't but there's always that risk depending on what other items are plugged in which is a grey area.
 
Hi. The boost function will rarely get used for 1.5kw rating as the heaters should store its heat from the ec7 supply so i wouldnt be too worried about using the ring for 2/3 units. There peak supply is mainly there for the programmer/room sensor/ fan facility.
I have been fitting the sunhouse version of the quantum heaters. They will save you a fortune as the dimplex quantums are overpriced imo.
 
Hi. The boost function will rarely get used for 1.5kw rating as the heaters should store its heat from the ec7 supply so i wouldnt be too worried about using the ring for 2/3 units. There peak supply is mainly there for the programmer/room sensor/ fan facility.
I have been fitting the sunhouse version of the quantum heaters. They will save you a fortune as the dimplex quantums are overpriced imo.
Sunhouse, Dimplex, Creda, Winterwarm, all the same heater, probably assembled by the same man
 

Reply to Quantum Heaters Dimplex Wiring supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
925
Firstly, thank you for taking the time to read this. I am not trained in electrics whatsoever, I am a just a home owner looking for advice. I...
Replies
2
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
207
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
689
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock