Discuss Queries regarding Inspection Report I've just had completed in the The Welcome Forum area at ElectriciansForums.net

Butch

-
Reaction score
11
Hi,
My first post so please go gentle on me!

I had an Inspection Report (EICR) completed on my house a week a go. It failed on two items:
1) Gap at the back of sockets in the utility (which I knew about, I meant to screw these down, but I only put them up loosely as I knew I had to take them down to plasterboard the wall at some point) - C1.
2) Excess copper showing - C2.

There is a comment on the report that the electrician was unable to complete the DEAD testing due to poor state of connections in the Consumer Unit even though the consumer unit did not fail the report.

The electrician is asking to be paid the full amount for the inspection even though as he states himself he was unable to complete the work. I assumed once I had resolved the C1 and C2 and CU connections (whatever he meant by that as he hasn't explained), that he would continue with the DEAD testing which would have been paid as part of the first invoice, however, he is advising that a full inspection would need to be carried out again at the full cost.

So, firstly, I am struggling to understand why he couldn't carry out the DEAD testing even when the CU didn't fail the test, was this a convenience thing as he stated on the report incorrect termination of neutral and earth conductors into their corresponding bars?

Secondly, once the C1 and c2 have been rectified, is it normal practice to do a complete test again or just re-check the failed items?

Does anybody know how long it takes to perform a DEAD test?

Also, the certificate he has issued has "This is not a valid certificate/report. This is a preview only" written all over it, making it difficult to read, again is this normal, will he issue the valid one when I have paid him?

I have gone back to the electrician with queries but it is almost like he can't be bothered to explain anything, I've asked him for locations of various things but he is very vague in his responses. Just wondered if this is normal practice.
 
Welcome to the forums.

I take the view the job isn't complete until the full certificate has been issued as that is what you've paid for.

Unless it's seriously bad, I wouldn't expect to complete a new inspection. I would issue certificates for the work carried out, but you wouldn't get a certificate that says satisfactory at the end of it. You'd have the unsatisfactory and certificates covering the work carried out to correct the issues.

Can you post a copy of the report (with identifying information removed) and possibly pictures of what it is he's saying require attention? Obviously only take pictures if it's safe to do so.
 
Its an EICR, basically a REPORT... its not a CERTIFICATE. Its not a case of a pass or a fail.
Its there to tell you, the customer, the condition of the installation and that some things may need attended to.
Whether you get them done or not is up to you.

That said, is the EICR been arranged so you can sell the property, or rent it out? In which case any dangerous faults would need repaired, with a test certificate that supercedes the remarks made in the EICR.

The only thing I can think of with the CU is it being a really old fusebox where the terminal screw heads have sheared off - meaning he cannot disconnect anything to do the testing properly.

The guy isn't being very professional saying he has to do another full test at full price again. That's just extracting the urine.
 
This is where I think people get upset and confused over EICRs as they are a report on the condition of an installation at a point in time.
Probably comes down to the actual agreement between the spark and customer and what the customers reqirements are. As SC above and I’m sure you’ll get some good pointers from the experienced sparks on here.
 
Hi, thanks for a quick response...

I wasn't sure if you wanted the entire report or just the bits where the electrician has made his comments and the list of failures, I've provided the latter but if you want me to post the full report I can do.

first page.JPG List of items.JPG
 
Before I carry out a EICR I always agree the extent of limitations with the client.

Im not sure why the electrician didn't carry out the dead tests if this was agreed. When the consumer unit is in a bad state I usally do ring continuity at a socket outlet.
Once the remedial work is you would be expected to recieve a EIC ( which covers the corrected work) and a covering letter which states the installation is now in satisfactory condition.
I wouldnt expect to pay for a EICR twice.
But Its easy to comment on this without seeing the reports.
 
Hi to all that have responded and thanks...

AJshep...you have said exactly what I would have expected, however, what if I carried out the remedial work myself, would this make a difference to getting it tested, would the remedial work and only the remedial work need checking or would it require an entire check again?
 
There are ways in which the dead testing can be carried out even when the terminations aren’t in their appropriate location as AJ said RFC can be done from a socket rather than the board and a global R1+R2 test can be achieved by isolating the DB and putting a jumper from the busbar to the earth bar then switching each MCB to the on position 1 at a time while the Main switch is obviously locked off then obtaining the readings it’s not hard and actually causes less disruption and is less likely to introduce faults than disconnecting one circuit at a time.
 
This is my take on the points raised.... Firstly, did you agree the limitations with him before hand?

Items....

1. C3 is fine, won't result in unsatisfactory
2. C3 is fine, won't result in unsatisfactory, however if that's the only reason he didn't do dead testing... he's a muppet
3, 4, 5 - I think one C3 would have been enough for the lack of labelling. Fairly common problem on older installs
6 - Guessing this is CPC sleeving... again, fairly common on older installs not to find any
7, 9, 10, 11 - Personally, I don't think these need to be listed as for existing installations this should usually be a limitation on the entire report. What I find quite interesting though is 16. He's obviously looked at enough to establish that in his opinion there is an excess of junction boxes (which are usually tucked away in the fabric of the build). However... this isn't strictly against the regulations. Being unable to access them for inspection purposes is (if they are screw type) but providing they are well terminated, an excess is not a breach of the regulations, it's just not good practice
12 - If I come across situations like that, I simply re-terminate and comment on a continuation page. It takes hardly any time.
13 - Did he say where?
14 - Loose accessories, justifies a comment
15 - Valid point
17 - I can't read

It's interesting he makes the point about knockout boxes and exposed live parts but doesn't list the junction box in the loft with no cover on it, just a comment.

At the very minimum, he could have conducted a global IR test on the whole installation. Would have been better than nothing, or could have pulled the fuses and just carried out a 250v L-E test for each circuit and then possibly a global N-E test and possibly even a by circuit L-N test (with all other neutrals connected). There are ways and means of getting some results if you're intent on doing the best job you can. I would caveat those results on a continuation page.

Please note.. these are my opinions only based solely on the content of the report.
 
New posts

Reply to Queries regarding Inspection Report I've just had completed in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
875
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
764
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
25
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
306

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock