Hi everyone,

I have what I'm sure is a very basic question that I would really appreciate some help on. I am a cider maker and recently purchased a new apple grinder that is manufactured in Germany and runs on 230v/50hz. I am wondering how I can use it here in the US? It came with a power supply that requires me to wire my own plug to it (not pictured below). But my question is, what do I need to do to make it functional here in America? Any and all help would be much appreciated. Thanks so much in advance,

jack
 

Attachments

  • IMG_0315.jpg
    258.9 KB · Views: 22
  • IMG_0318.jpg
    353 KB · Views: 20
  • IMG_0317.jpg
    363.7 KB · Views: 20
  • IMG_0316.jpg
    228.3 KB · Views: 19
I’m not sure you can.
America 2-phase is 220v, and the frequency is 60Hz.

I’m sure @Megawatt will correct me if I’m wrong there.

There may be an American version, or it might be an easy job to swap out the motor
 
the rating plate says 50/60hz
220v is probably close enough for the motor to be run without problems.
you need a 220v outlet and a cable made up to connect it.
often your tumble dryer outlets are 220v if I recall?
 
Typical residential supplies in the USA are 120V / 240V split-phase with two hot wires and a neutral. Domestic appliances typically use one hot and neutral for 120V, but stoves, dryers, A/C etc use the two hots to supply 240V and this configuration will power your apple grinder.

You will need a 240V grounded outlet to plug the machine into; it does not matter whether the outlet has a neutral or not, as the machine won't need it, only the two hots and ground. Therefore either of the two common types of 240V receptacle, type 6 (without neutral) or type 14 (with neutral) will suit. Then you would make a cable from a matching plug, (e.g. if you have a 14-20R receptacle then a 14-20P plug) to Schuko inline coupler to fit the machine. The line and neutral terminals of the coupler will connect to the X and Y terminals of the plug. Because the inlet on the machine is non-polarised, it does not matter that both wires will be hot, instead of hot and neutral.

Larger 240V outlets such as 30A and 50A rated types used for stoves and dryers will supply the necessary power but the breaker will not offer adequate protection to the machine cable. You would need to down-rate the circuit to say 20A or add a local breaker box with a smaller outlet.

Ensure codes are met regarding ground fault protection if required.
 
Typical residential supplies in the USA are 120V / 240V split-phase with two hot wires and a neutral. Domestic appliances typically use one hot and neutral for 120V, but stoves, dryers, A/C etc use the two hots to supply 240V and this configuration will power your apple grinder.

You will need a 240V grounded outlet to plug the machine into; it does not matter whether the outlet has a neutral or not, as the machine won't need it, only the two hots and ground. Therefore either of the two common types of 240V receptacle, type 6 (without neutral) or type 14 (with neutral) will suit. Then you would make a cable from a matching plug, (e.g. if you have a 14-20R receptacle then a 14-20P plug) to Schuko inline coupler to fit the machine. The line and neutral terminals of the coupler will connect to the X and Y terminals of the plug. Because the inlet on the machine is non-polarised, it does not matter that both wires will be hot, instead of hot and neutral.

Larger 240V outlets such as 30A and 50A rated types used for stoves and dryers will supply the necessary power but the breaker will not offer adequate protection to the machine cable. You would need to down-rate the circuit to say 20A or add a local breaker box with a smaller outlet.

Ensure codes are met regarding ground fault protection if required.
I have to agree with @Lucien and good luck with your project
 
Typical residential supplies in the USA are 120V / 240V split-phase with two hot wires and a neutral. Domestic appliances typically use one hot and neutral for 120V, but stoves, dryers, A/C etc use the two hots to supply 240V and this configuration will power your apple grinder.

You will need a 240V grounded outlet to plug the machine into; it does not matter whether the outlet has a neutral or not, as the machine won't need it, only the two hots and ground. Therefore either of the two common types of 240V receptacle, type 6 (without neutral) or type 14 (with neutral) will suit. Then you would make a cable from a matching plug, (e.g. if you have a 14-20R receptacle then a 14-20P plug) to Schuko inline coupler to fit the machine. The line and neutral terminals of the coupler will connect to the X and Y terminals of the plug. Because the inlet on the machine is non-polarised, it does not matter that both wires will be hot, instead of hot and neutral.

Larger 240V outlets such as 30A and 50A rated types used for stoves and dryers will supply the necessary power but the breaker will not offer adequate protection to the machine cable. You would need to down-rate the circuit to say 20A or add a local breaker box with a smaller outlet.

Ensure codes are met regarding ground fault protection if required.
Thanks so much for taking the time to explain this. A friend recommended I use a step down transformer and a normal 120v outlet, would this be advisable?
 
That is also possible, although it is a step-up transformer you need (120 -> 230V) not step-down. The machine is rated at 1900W but we have to guess the power factor because it does not state the current (The current on the starter label is the starter rating, not the motor.) If we call the pf 0.85 at full load then the load on the transformer will be 1900/0.85=2.2kVA so you would want a transformer with a continuous rating of 2.5kVA or more. If the transformer efficiency is 90% then at full load, based on that guess of power factor, the current on the 120V input side will be just over 20A. In theory this is too high for any normal outlet branch circuit so you would need to put in a 30A 120V circuit to feed the transformer. In practice it is not going to run at full load continuously and we don't actually know the running current. But it's worth drawing that possibility of marginally overloading a 20A 120V outlet to your attention.
 
If it's a 'dumb' or anaolgue machine then as per Lucien it should run on the USA 240v split phase. If it's got internal electronics with any kind of coms it may need a low N-E voltage (<1.5v) in which case it might not work correctly or may even be damaged by a split phase supply. If it's got complex electronics built-in I'd play it safe by using an isolating transformer with one of the output legs referenced to ground.
 
That is also possible, although it is a step-up transformer you need (120 -> 230V) not step-down. The machine is rated at 1900W but we have to guess the power factor because it does not state the current (The current on the starter label is the starter rating, not the motor.) If we call the pf 0.85 at full load then the load on the transformer will be 1900/0.85=2.2kVA so you would want a transformer with a continuous rating of 2.5kVA or more. If the transformer efficiency is 90% then at full load, based on that guess of power factor, the current on the 120V input side will be just over 20A. In theory this is too high for any normal outlet branch circuit so you would need to put in a 30A 120V circuit to feed the transformer. In practice it is not going to run at full load continuously and we don't actually know the running current. But it's worth drawing that possibility of marginally overloading a 20A 120V outlet to your attention.
Makes sense, thank you again for taking the time to explain everything so thoroughly, I appreciate it! I am unsure that I have a 240v outlet where I will be making the cider so this seems like it might be the only option
 
That is also possible, although it is a step-up transformer you need (120 -> 230V) not step-down. The machine is rated at 1900W but we have to guess the power factor because it does not state the current (The current on the starter label is the starter rating, not the motor.) If we call the pf 0.85 at full load then the load on the transformer will be 1900/0.85=2.2kVA so you would want a transformer with a continuous rating of 2.5kVA or more. If the transformer efficiency is 90% then at full load, based on that guess of power factor, the current on the 120V input side will be just over 20A. In theory this is too high for any normal outlet branch circuit so you would need to put in a 30A 120V circuit to feed the transformer. In practice it is not going to run at full load continuously and we don't actually know the running current. But it's worth drawing that possibility of marginally overloading a 20A 120V outlet to your attention.
Another question, if going the transformer route what type of plug should I wire to? I have a friend who has offered to let me use this: https://www.amazon.com/Rockstone-5000-Watt-Transformer-Converter/dp/B00J0CF8W4
 
Another question, if going the transformer route what type of plug should I wire to? I have a friend who has offered to let me use this: https://www.amazon.com/Rockstone-5000-Watt-Transformer-Converter/dp/B00J0CF8W4
That converter has a 'universal' output socket ?, which will accomodate a European Schuko male plug, the same format as is fitted to your apple grinder, so that seems an obvious choice.

A US 3-pin plug (as is fitted to the converter) might be a bad idea because someone is bound to plug your grinder in to a 110v socket at some point, and wonder why it doesn't work properly.
 
That converter has a 'universal' output socket ?, which will accomodate a European Schuko male plug,
Well the pins of the plug will fit but it won't make contact with the side earth contacts so not a good choice!. A NEMA 6-15P or 6-20P 240V plug might fit although as per the smiley those sockets don't always make good contact with anything. A UK 13A 240V plug would probably be OK.

Those low- cost transformers are a bit of a con, their rating is lower than the number suggests. E.g. the description for the 5kVA version says it's only suitable for appliances up to 3kVA. That makes it a 3kVA transformer in my book. But it should do your job, 120V input plug overload possibility notwithstanding.
 

Reply to Question about using a 230v appliance here in the USA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
Good day all, I'm writing from the Commonwealth of Dominica (NOT Dominican Republic) where we have single phase 230V, 50Hz. I'm managing a...
Replies
3
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
848
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
I am currently looking to add 12v led cob strip lights to my mother's kitchen but confused what I need. There are currently mains wires under the...
Replies
2
Views
595

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock