Hi all,
I have worked out the volt drop on other questions using the formula mVxAxM.
had no issues, but this question below has just fried whats left of my brain, I have the answer because i got it wrong,
but how do you work this one out??

Being Dyslexic i do sometimes read the questions all wrong and am sure i am missing something simple here.

Voltage drop of a single-phase circuit supplying a bread oven is to be verified as part of periodic inspection and testing within a bakery.

The circuit has a measured R1+Rn value of 0.40 Ω and an Ib of 29.6 A. The circuit protective device has an In of 32 A.
The installation forms part of a public 400/230 V TN-S system. What is the calculated value of voltage drop?

a) 11.8 V
b) 13.5 V
c) 14.2 V
d) 14.8 V
 
If I had to guess I'd say it's to do with cable resistance times Length (You're given R1 RN) however there is no distance listed, nor cable type used so I'm a bit stumped.

Design current 29.6A, Voltage 230/400 gives 7.7Ω @230v and 13.51Ω @400v (R=V/I)

Using the resistances above, check against (purely a guess here) resistence per metre to get the length and possibly cable type, then you should have the required info to calc volt drop.
[automerge]1596551079[/automerge]
Try with Vd = (R1+Rn)x1.2xIb
 
exactly what i though, 11.84v

but the answer sheet says i was wrong, it is 14.2v

Is it the right answer sheet to the paper? - which paper is it, I have just looked at C&G web site, question 27 on paper 1.3 appears to be the same question.

The 1.3 answer sheet gives it as answer b (which is also wrong!)
[automerge]1596553244[/automerge]
Multiply the resistance by 1.2 for temperature correction under load ?

that looks the case to me.
 
When I said multiply by 1.2 for temperature, that was a shot in the dark, having looked at the books I can find nothing to substantiate a factor of 1.2. What does your Tutor say?
 
R1+Rn x design current = volt drop at nominal temp

(R1xRn x design current) x1.2 = volt drop at 70°c

So yes correct answer is 14.2 volts.
 

Reply to Question on volt drop from 2391 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
655
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
800
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
786
Hi all, I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone...
Replies
20
Views
5K
Morning team Question about volt drop. I presume I am missing something here. So firstly the facts out the OSG. Table 7.1, page 66, lighting...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock