Discuss Question regarding 400V three phase lighting connected in Delta, without Neutral. in the Commercial Electrical Advice area at ElectriciansForums.net

A

AReynolds

I am in the process of designing the electrical installation of a community centre, and have a question about the provision of three phase lighting for a large function room containing 18 36W LED fittings. All of the light fittings are to be switched simultaneously. Would it be possible to connect these lights in a three phase Delta configuration using 400V LED driver units, by connecting 6 light fittings/Drivers to each line, thereby ensuring a constant balanced load on each line? Presumably, I would not need to provide a neutral for each line, and could get away with just providing earthing for each fitting? Does anyone think that this design would be unsuitable?
 
how can a single phase load function without a neutral, unless it's 415V s.p.
 
Ok because of the phase angle/voltage difference at each 120 degree angle but I can see that on say a single circuit like a water heater but separate circuits, that works? I can't quite think this out. Mmm maybe...why not indeed or even why
 
the singlephase load requires 240V. the only way to get that from a 3 phase 415V supply is Ph -N, N being the star point.
 
If there is such a thing as a 400V LED driver, then yes. There's no need for a neutral and no need for loads to be balanced. Just connect them between any two lines and that's that. I'm not familiar with units that take 400V AC input though. And, uh, why?
 
they'd say you've put 400v across our 230V driver. warranty is void.
 
the singlephase load requires 240V. the only way to get that from a 3 phase 415V supply is Ph -N, N being the star point.
Agreed but the star point requires no connection to neutral. I regularly used to demonstrate this by having three 60w lamps connected across three phases and the neutrals floating and just connected together.
 

Reply to Question regarding 400V three phase lighting connected in Delta, without Neutral. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
A
the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3...
Replies
4
Views
468
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hello everyone! I have a question regarding the electricity supply and the maximum demand. One energy utility supplies an 18 kVA maximum...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock