I have always been a bit confused about boxes 10,12 and 13 in the example of a completed 'Form 4 - schedule of test results'.

I understand why the value we get for R1+R2 (when measured at a socket) is a quarter of the end to end resistances, but why on the form is this not more clear?

Box 10 (R1) and Box 11 (R2) do not equal Box 13 (R1 + R2). Again I understand why, but it just seems wrong to have a box for R1 and a box for R2 but adding them together is not R1+R2.

Its annoying :cuss:

The form is correct as boxes 10,11 and 12 are asking for the end to end resistance for r1 , rn and r2 , these are all end to end resistances as in step 1 of the ring final circuit test to check that they are substantially the same , the true R1 + R2 of the circuit is established in step 3 by cross connecting R1 and R2 and measuring at each socket outlet this goes in box 13 . If you add up box 10 and 12 and divide by 4 this cross references your R1 and R2 .
 
It's really quite simple, if doing an EICR the installation has power so only need to do end to end to make sure it's a ring then do. ZS at each socket. If no power then you have to do R1+R2 and work out ZS by adding it to ZE.
 

Reply to R1 + R2 does not equal (R1+R2) in example in On Site Guide. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have...
Replies
9
Views
7K
Be warned it you are tempted by shortuts. I know in domestic work on old houses, we often have a race against the clock, and it can get stressful...
Replies
6
Views
2K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
V
Why is the value of r1plus r2 a quarter of the end to end resistances added together in a ring circuit
Replies
6
Views
927
sedgy34
S
Z
Dear Friends I have booked my 2391 exam on October 18th for third time and this is my last chance to pass it. I have about five past exam...
Replies
44
Views
15K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock