Yes. thats fine.

These are the sheath CSA's that you will need to note on the test form......


Physical cross sectional area of MICC/PYRO copper sheath for use as CPC.


2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2

2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2


2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2


2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2

2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2

2L4 ****** 11 mm2
2H4 ****** 16 mm2

2H6 ****** 18 mm2
3H6 ****** 20 mm2

2H10 ****** 24mm2
3H10 ****** 27mm2

2H16 ****** 30mm2
3H16 ****** 34mm2
 
Thanks for that Lenny, may be usefull in the future.We just write 'MICC' or 'sheath', and have never been picked up for it, do you always write the size, or a combination of the two?
 
Last edited by a moderator:

Reply to r1 r2 testing on micc cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
616
  • Article
Electrical2Go now stocks a selection of Super Rod products, designed to help you save time on cable installations and more! One of our best...
Replies
0
Views
909
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
901
Hello, Hoping to get some advice on R1 + R2 radial testing and best practise. When doing R1 R2 instead of taking cables from mcbs/rcbos and the...
Replies
1
Views
2K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock