Discuss RCBO on TT earthing is it safe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Yr ys

-
Reaction score
4
Is it safe to use single pole RCBOs on a TT earthing system without an rcd and just a double pole breaker?

What would the max allowable earth resistance be to cut out a earth to neutral fault?
 
Thank you for your kind reply.

Sorry I meant because the rcbos are single pole it wouldn't disconnect the neutral due to a earth to neutral fault. It would detect it however and disconnect the phase only. Am I right? And a double pole isolation is good enough no need for an rcd?
 
Thank you for your kind reply.

Sorry I meant because the rcbos are single pole it wouldn't disconnect the neutral due to a earth to neutral fault. It would detect it however and disconnect the phase only. Am I right? And a double pole isolation is good enough no need for an rcd?
Yes, that’s right.
 
Double check manufacturers instructions if using RCBOs on a TT system as some state that certain types are not suitable for use such as Schneider single pole devices.

You do need a method of isolating all live conductors on a TT system but this can be done at source by one single pole device, however I personally would install double pole devices on TT systems on all final circuits as there could be quite a large potential difference between neutral and earth and a double pole device would allow you to safely isolate both live conductors on a final circuit.
 
Is it safe to use single pole RCBOs on a TT earthing system without an rcd and just a double pole breaker?

What would the max allowable earth resistance be to cut out a earth to neutral fault?
No offence to you either chap, just having a giggle over a late lunch :)
 
Double check manufacturers instructions if using RCBOs on a TT system as some state that certain types are not suitable for use such as Schneider single pole devices.

You do need a method of isolating all live conductors on a TT system but this can be done at source by one single pole device, however I personally would install double pole devices on TT systems on all final circuits as there could be quite a large potential difference between neutral and earth and a double pole device would allow you to safely isolate both live conductors on a final circuit.

Hi and thanks for your kind reply

You mean isolate all circuits with one double pole breaker right?
 
Thank you for your kind reply.

Sorry I meant because the rcbos are single pole it wouldn't disconnect the neutral due to a earth to neutral fault. It would detect it however and disconnect the phase only. Am I right? And a double pole isolation is good enough no need for an rcd?

This problem is present with SP RCBOs regardless of which earthing system is in use.
The RCBO will detect the fault on the N and disconnect the L.
 
All good.


Why do some manufacturers specifically say do not use on TT systems?

I couldn't say for certain, presumably it is to cover their arses in case of issues, also they probably sell the same devices in country's where it is not allowed and its cheaper to make all the instruction sheets the same than print a different one for every country.

Also some manufacturers specify lower Zs limits than the often quoted 1667.
 

Reply to RCBO on TT earthing is it safe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
572
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
601
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
OSG Pg.40 says: '[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault...
Replies
79
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock