Thank you Westward10. Is it peculiar to this brand?It needs a load through the sensing coil from the line terminal as the imbalance is detected where the conductor passes through the tunnel to the terminal. Testing direct to the terminals bypasses this. Get an extension socket with the three wires and connect into the rcbo if you want to test at the board.
Thank you for that. Is it peculiar to just this brand or a certain age of RCBO?It needs a load through the sensing coil from the line terminal as the imbalance is detected where the conductor passes through the tunnel to the terminal. Testing direct to the terminals bypasses this. Get an extension socket with the three wires and connect into the rcbo if you want to test at the board.
As far as I know it is just those retrofit rcd pods from Memshield 2. The pod fits a standard mcb but you can also find them in Memera 2000 as they are a similar device.Thank you for that. Is it peculiar to just this brand or a certain age of RCBO?
CheersAs far as I know it is just those retrofit rcd pods from Memshield 2. The pod fits a standard mcb but you can also find them in Memera 2000 as they are a similar device.