Hi I was testing a large holiday let property which has a three phase supply and dB
Now the original install was in 2012 and electrically is well done but poorly designs on socket circuits all rcbo are type c and only on socket circuits I am over the max permitted zs I would recommend change to type b but looking for some regulation to note on test cert
 
You can disconnect on the RCD side of the RCBO to meet the regulations, as you generally have to for a TT system.

I would generally prefer to meet disconnection on the OCPD side of things on TN systems if at all practical, just as i believe the thermal-magnetic trip side is simpler and more reliable than the RCD electronics. But it is not an absolute must.

How far off meeting Zs are you?

Do you know if there are any other reasons for putting the sockets on C-curve breakers, such as it is used for motor loads with high start-up currents?
 
Last edited:
You can disconnect on the RCD side of the RCBO to meet the regulations, as you generally have to for a TT system.

I would generally prefer to meet disconnection on the OCPD side of things on TN systems if at all practical, just as i believe the thermal-magnetic trip side is simpler and more reliable than the RCD electronics. But it is not an absolute must.

How far off meeting Zs are you?

Do you know if there are any other reasons for putting the sockets on C-curve breakers, such as it is used for motor loads with high start-up currents?
Thanks for the replay
Supply is a tncs with a ze of 0.15
At 250v
No just standerd domestic items realty on socket most socket circuits
Exsept garage has a small pump for the private water supply I think that's all that was available for rcbo at the time of install for the crabtree distribution board and looks like the electrician who designed the installation made poor choice of that equipment
Of the top of my head one socket circuit zs was 0.83
 
Thanks for the replay
Supply is a tncs with a ze of 0.15
At 250v
No just standerd domestic items realty on socket most socket circuits
Exsept garage has a small pump for the private water supply I think that's all that was available for rcbo at the time of install for the crabtree distribution board and looks like the electrician who designed the installation made poor choice of that equipment
Of the top of my head one socket circuit zs was 0.83
Also no rcd uplift I use a Megger 1721
And high quality crabtree rcbo from 2012
 
Of the top of my head one socket circuit zs was 0.83
With Ze = 0.15 you have R1+R2 of around 0.68

Assuming 2.5mm T&E radial is 19.5 ohm/km then you are looking at around 35m length, so it a sane result, but in that case it ought to be on 20A which as maz Zs of 0.87 ohm so met?

If it was a typical 32A RFC on 2.5mm then r1+r2 = 4 * (R1+R2) so about 140m which is fairly long.

It is not big issue but may suggest something else is not quite right?
 
Also no rcd uplift I use a Megger 1721
And high quality crabtree rcbo from 2012
All dead R1 R2 an
With Ze = 0.15 you have R1+R2 of around 0.68

Assuming 2.5mm T&E radial is 19.5 ohm/km then you are looking at around 35m length, so it a sane result, but in that case it ought to be on 20A which as maz Zs of 0.87 ohm so met?

If it was a typical 32A RFC on 2.5mm then r1+r2 = 4 * (R1+R2) so about 140m which is fairly long.

It is not big issue but may suggest something else is not quite right?
It is a massive property and and every other test is consistent most of circuits would be fine on a 20 amp rcbo apart from kitchen i just think it was poorly designed in the first place. For example there is a 50 amp rcbo feeding 25mm swa to the annex / garage with a 14 way high integrity d.b with 4x rcbo and 2 X rcd and rest MCB
 
It probably was poorly designed but when it comes to testing it is what it is. Although not in your case a high Ze may leave you with no choice but to rely on an rcbo for fault protection I personally wouldn't look into it too deeply.
 

Reply to Rcbo with higher than permitted zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
507
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock