JS118m

DIY
Reaction score
0
I recently cut through the live 240V power cable of a plane the tool is double insulated, the blade exposed and combined both conductors. The supply is protected by a 30ma RCD and 30Amp MCB (10 yera old installation), the RCD didn't trip, it does trip when the test button is pressed. Could it be the case that in this situation the RCB won't trip or is it likely there is some sort of fault in the system? Thanks
 
RCDs fail (get stuck) , I have tested several RCDs that have failed to trip under test...
they are not perfect

The very reason they have a test button! Not that most folk do...

Compared to the over-current protection of a MCB, the electronics for the RCD action is significant more complex and so more likely to fail.
 
Thanks - so I guess if I'd picked the exposed live up it would have?

If you received an electric shock of high enough magnitude it should have done yes.

A 30mA RCD is designed to disconnect the power if a person receives a bad electric shock before it becomes fatal for the majority of healthy people.
 
Also the RCD action only protects you if you touch live and are otherwise grounded (typically folk chopping cables while in the garden, previously a very common way to get electrocuted).

If you are unlucky enough to touch both live and neutral the RCD sees nothing wrong, so you fry. If you are lucky and it is only on one hand you probably will be able to get away and injury is probably quite local, but hand-to-hand is often fatal.

In the old days of working on valve radios, etc, with their 200-400V HT supply it was common advice to keep one hand in your pocket!
 

Reply to RCD didn't trip when live conductors cut in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K
Hello. we have had a few powercuts over past few months and am in middle of one at the moment where power has gone off a few times while DNO are...
Replies
8
Views
4K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top