Discuss rcd incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
136
hi guys i need some help..

my board at home has a 80amp 30ma rcd incomer without a incomer dp switch.

about 10 used circuits ans about 4 spare.

i get some tripping problems so i want to change the rcd as its hard to reset sometimes and crap quality

q- can i use any brand rcd or do i have to use the crap protek one to match the board.
also should i fit a dp incomer as well.

also my combined amps on the whole mcbs add up to about 128 amps! this is on a 80a rcd is this overloaded ..

thanks in advance...
 
Switch is probably not overloaded as diversity comes into play. Although all the breakers add up to 128A you hopefully would not be using any of them to max capacity at any one time if at all.

You can use any RCD as long as it fits, the problem you may have is getting one that does, they have a tendency to be just a little different to make fitting the busbar a problem.

Lenny's idea is better.
 
BG do a tasty board at a good price.
 

Reply to rcd incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
546
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock