Forgery

I isolated a lighting circuit, confirmed and locked off. Went to fixture, rechecked for any voltages using a combined clamp meter, looked good carried out removal.

Prior to this, customer upstairs working on laptop was warned I was working on the lighting circuit, but should not effect her work on laptop, but perhaps it may be wise to work from battery source of laptop only.....which was just as well!

Everything ok until I pull through cable to re-route and pop off goes main RCD.

Basically, I have since discovered checking with the meggar that I have 1volt on the neutral, so when it touched the CPC it knocked out the RCD, could be borrowed neutral, insulation problem or is it something else to do with TT systems, interested to know what you think and or am I just being thick .

Cheers , insults welcomed!
 
as all neutrals are common at the cu locking of the mcb only cuts the live. therefore you will get a few mA on your neutral thats why your rcd tripped
 

Reply to RCD on TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
715
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
922
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
865
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock