Search for tools and product advice,

Discuss RCD or Main switch in garage board in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi this may be a simple answer to my question but I can't find the answer in the regs

If im fitting a garage board from a consumer unit with RCD protection do I need to have RCD protection in the garage board?

I'm guessing I don't need an RCD at the garage board but I can't find a definite answer in the regs

Thanks in advance
 
It depends on the wiring type between the house and the garage.
Ie, twin and earth buried in wall less than 50mm, then it needs an rcd to protect it.
SWA, you could have an mcb at the house, and rcd in the garage.

Even then, the garage could be an rcd mainswitch with individual circuit mcbs or a regular mainswitch and rcbo’s.
 
As already alluded to, more info is needed to answer.
For all we know it could be an 100ma main switch RCD for a TT setup in the house.
It's a 30ma type F RCCB in the house board 40A MCB with 10mm cable to Garage board not actually fitted in the garage but in a kitchen cupboard to feed an ASHP, control panel and a heat recovery unit
 
I'm guessing I don't need an RCD at the garage board but I can't find a definite answer in the regs
In general terms, the relevant regs would be in the following areas:
1) loads requiring an RCD
2) Whether the prospective fault current will operate the upstream breaker because the Zs is low enough, or whether an RCD is needed for fault protection
3) Whether RCD protection is required due to the way the cable is run (Impact Protection)

t's a 30ma type F RCCB in the house board 40A MCB with 10mm cable to Garage board not actually fitted in the garage but in a kitchen cupboard to feed an ASHP, control panel and a heat recovery unit
I'm fairly sure this would be adequate in practise (interesting it's a type F).

The only (subjective) question in my mind is whether there's any possible better design so you aren't adding even more loads to a common RCD.

If the distribution circuit doesn't require an RCD for impact protection or fault protection (e.g. it's SWA or is not buried in walls at all and it's not a TT supply) then I'd probably be looking at supplying it from a non-RCD protected MCB or split tails and fuse, and have the RCD protection on the final circuits in the garage board (RCBOs).

(just noticed @littlespark said most of this too)
 

Reply to RCD or Main switch in garage board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
905
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
799
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi all I am after some advice on an installation I have coming up. Its a new TP+N circuit in SWA (13m run clipped direct) for a 22kW Tesla wall...
Replies
1
Views
188
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
467
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top