Search the forum,

Discuss RCD protected? in the Australia area at ElectriciansForums.net

Reaction score
0
Hi guys,

I need a little advice - have attached photo...

I need to upgrade this fuseboard to Current regulations - customer cannot afford to replace CU with 17th edition split load board. can I move the RCCB to next to the main switch to protect all the circuits? Or can I add another RCCB to make it split load?

She wants cheapest option to bring if up to regulations. Any advice is much appreciated!

Kelly x

Can't upload photo with mobile so will upload with computer in 2 mins!!
 
heres photo of the CU - ta ;)
 

Attachments

  • photo.jpg
    269.3 KB · Views: 70
You could maybe fit more circuits on to the RCD and fit a couple of rcbo's say for the lights(but they can be expensive) I woul not fit them them all from the one rcd as it is only 63A max load on it and everthing would go off. I wouldn't recommend making it a dual rcd board as there probably would only be one neutal bar. Why does it need bringing up to cuurent regs? I would try and get the sockets rcd protected as a minimum. If no work has been carried out the Rcd issues on lights etc would be a reg change just check that bonding main and suplimentary is carried out. Fit some blanks as well.
 
that is a starbreaker board, because of the construction of the busbar,i donb't think you can fit a second RCD. you could easily move some MCBs from the unprotected sise onto the RCD, or fit RCBOs.
 
Why do you need to change the board? Current regs also say tat cate must be given to discrimination (or words to that effect) so one rcd will not be good enough. Put in at least 1 rcbo on one light circuit and move rest of circuits onto the rcd (assuming your diversity calcs say a 63A rcd is ok).
 

Reply to RCD protected? in the Australia area at ElectriciansForums.net

Similar Threads

My 1990 property does not have the lighting circuits protected by the Distribution Board RCCB.Only the power circuits are protected.If I get a...
Replies
1
Views
987
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
2K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock