Dean31

Hi Guys,

Need some advise on RCD protection, I have just tested 112 rooms in a Travelodge in Wales and there is no RCD protection on the bathroom lights, the ceiling is over 2.25m and the light fitting is a L.E.D class 2.

Looking in the regs in section 701 & 415 and from posts I have read on here they need RCD protection but I just wanted to get a few more opinions as the hotel is only 5 years old and surely this wouldn't have been missed when designed.

Many thanks
 
If you'd have said domestic, to be honest, i'd of said forget the RCD, 2.25m high ceiling, Class 2 IP44 light fittings, what's the point!!

But it's relating to a hotel, which puts a whole new dimension on the word Safety in my book!! As daft as it may seem, you'll need to give these bathroom lights additional RCD protection, if only to cover your arse!!!
 
I am not sure, the bathrooms are completely tiled so unable to remove units to see, they are just shower cubicles and no bath. They only thing I can see from the riser cupboard on the corridors which on some of the rooms are directly behind the bathroom are earthed bolts coming through the wall.
 
Thanks mate that's what I thought but thought I would see what others thought before I put in a quote for 112 RCBO's which will not be cheap.
 
I am not sure, the bathrooms are completely tiled so unable to remove units to see, they are just shower cubicles and no bath. They only thing I can see from the riser cupboard on the corridors which on some of the rooms are directly behind the bathroom are earthed bolts coming through the wall.

Any chance of a photo or two of this earthing bolt you're talking about, ....i'm intrigued?? By the way, if you haven't dropped the light fittings , how do you know for sure they are class 2 fittings??
 
Hi Guys,

Need some advise on RCD protection, I have just tested 112 rooms in a Travelodge in Wales and there is no RCD protection on the bathroom lights, the ceiling is over 2.25m and the light fitting is a L.E.D class 2.

Looking in the regs in section 701 & 415 and from posts I have read on here they need RCD protection but I just wanted to get a few more opinions as the hotel is only 5 years old and surely this wouldn't have been missed when designed.

Many thanks

This could be 2008 borderline -if the '5 years old' is estimated
The lights are definitely mains voltage (not elv), yes?
No certification from new install?
 
Last edited by a moderator:
i would assume thatr there are several rooms on a circuit so 1 RCBO could well protect 10-12 rooms' lighting circuits.
 

Reply to RCD protection on bathroom lighting. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For the bathroom, want them matching and one needs to go over the shower. Also need to be ok with insulation over the top. Ideally fit in the...
Replies
2
Views
225
I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
Replies
19
Views
1K
Sorry no photos, but I’ll explain best I can. Turn on the switch, I’m not getting any light. Apparently a new fitting. Description…. A white...
Replies
3
Views
300
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
973
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
283

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock