Hi Guys, I'm new to the forum and just wanted to say hello and if I may, ask for any help and advice as it would be really appreciated. I'm aware that the latest electrical regulations state that circuits within a bathroom/shower room/en-suite, need to have RCD Protection. However, where would you practically locate these RCD units? For example, one of the units to be fitted is for a Saniflo and because this is being installed within a wall void, the RCD Spur will be located adjacent to the actual Saniflo because it's out of sight, but easily accessible. But what about the RCD's to protect the Lighting and Extraction System? The consumer unit does have MCB's which could be replaced with RCD type, but I would rather go for localised RCD's since the Saniflo installation manual states that it must have one anyway. I'm thinking of two additional local RCD Spurs, one to feed the (2) IP65 Ceiling Lights and an illuminated wall mounted (infra red touch controlled) mirror, and another one, to control the extraction system which I want to keep separate so that I can have it switch operated (so that it doesn't automatically turn on when the light switch is turned on, causing unnecessary noise during the night) via either a ceiling pull switch, or (most likely) an external wall mount switch. I know that I could just mount the RCD spurs directly above the two external wall mount switches for example, but they aren't very aesthetic, so maybe I could mount them within the stud wall and access them via a plastic wall panel? Just looking for ideas to be honest. Steve
 
easiest solution would be to fit RCBOs to the lighting circuit ( lights and extraction fan) and to the RFC? that the saniflo is connected to. this way, you'd be giving additional protection to the complete circuits involved. also it's far neater as regards not having RCD FCUs screwed to the walls all over the place.
 
SFT223

after youve paid for three RCD FCUs you'll almost cover the cost of a new budget board loaded with RCBOs....

it really is the way forward.

i have fitted RCD FCUs in the past but looking back it was....a bodge.
 

Reply to RCD Protection Units For En-Suite in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
384
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
663
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
817
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
513
i am wiring up a new en-suite: it is about 1.7m square, shower cubicle in one corner, toilet in other, door between, basin next to shower. I will...
Replies
2
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock