I am installing some sockets in a room using dado trunking but in order to get the ring from the CCU to the trunking i have had to pass through a wall, im aware that cables buried at less than 50mm require to be RCD protected. The ring willl be suppling computer equiptment and will be lablled that is its only intended use, would i still need to RCD/RCBO this circuit?
 
In short, yes, you would `if` the cable is concealed in the wall <50mm (or wall contains metal parts)



RCD protection (by RCCB or RCBO) is required for all general use socket outlets, but a relaxation of this is permitted for s/o supplying a specifically labelled outlet for `a particular item of equipment`

but only if RCD protection is not required on other grounds (i.e. cables concealed <50mm)

So, two quite seperate regs to be satisfied there - & not to be blurred into one.

Its then on you to argue whether equipment & installed cables fit definitions for exemption, or not.

IMHO, eclectic PC kit doesn`t equal `a particular item of equipment` - but maybe thats just me :cool:
 
I would agree with electrical, if the socket circuit is complied of standard sockets just feeding some pc's then RCD to not rcd then you need to be looking along the lines of a special socket and plug set up ie with a t shaped earth pin, you say the wiring just goes through the wall not actualy burried along the wall?
 
is concealed in the wall ie. less than 50mm the same as passing through the wall

surely you cant hit a cable goin away from you
 
"is concealed in the wall ie. less than 50mm the same as passing through the wall?"

No, it isn`t


"surely you cant hit a cable goin away from you"

Bet you could if you really tried :D

But, as you alude, cables passing thru a wall & those concealed along the wall are two different things & have different RCD requirements.
 
Is this domestic or commercial? Things are more leaniant for commercial.
How many computers? If there are several you may end up causing unpleasant harmonics that will need filtering.
 

Reply to RCD Protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
546
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
462
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock