Discuss RCD Question in the Australia area at ElectriciansForums.net

Reaction score
16
Hi Guys, a quiery for you, ( by the way I live in Western Australia) I was doing some work at the house today and was disconnecting some sockets for renovations, so i isolated the circuit but had to cut the T&E to get it out at the other end. Now the thing is that I have 3 phase incoming red phase protected by DP RCD, White(Yellow)phase the same and blue phase non protected circuits, each rcd protected phase has a mixture of power and lighting(thats the regs over here)
So when I cut the T&E I was expecting the white phase RCD to trip out but it didn't so i stripped it back and touched N and E together but no trip. I put a socket back on and plugged in my Robin digital RCD tester and did the x1/2 test which didn't trip(correct) then x1 at 30mA and tripped at 18mS at 0 degrees and 9mS at 180 degrees.
I've been sparkying for 22 years and have always believed N and E shorted out will trip an RCD, correct me if i'm wrong but can anyone shed some light on this.
The type of earthing arrangement over here is (crap) TPandN supplied by service provider then the spark installs an earth rod with a 6mm from that to the earth bar then an MEN link from earth bar to N bar.
Thanks
 
If we are going to assume everything is ok with your system, and it looks like it then off the top of my head I can only think that perhaps when you touched N/E together on the circuit it never tripped because the mechanism had some dust or was siezed.

Do you regularly test the button? After doing the tests with the tester, does the RCD trip now when you touch N/E together?

I would also ramp test the RCD if you can, the RCD tester will give you the timings, a ramp will tell you the trip mA.
 
Thanks for the replies guys, This afternoon i did some poking around , I disconnected the main earth from the earth rod , everything about it was very corroded, rubbed it back to shiny copper , remade the end and fitted a new clamp and hey pesto all fixed, it must have been like that for years(very worrying to think about it). Went back to the board and shorted out Earth to red phase neutral bar and white phase neutral bar and both RCD'S tripped.
This just shows that you can't be to reliant on testers , as my rcd tester was still causing a trip.
 
that may be because when you shorted the N and E, the E was not earthed due to the corrosion you found. therefore the RCD did not see it as a fault.
 
Thanks for the replies guys, This afternoon i did some poking around , I disconnected the main earth from the earth rod , everything about it was very corroded, rubbed it back to shiny copper , remade the end and fitted a new clamp and hey pesto all fixed, it must have been like that for years(very worrying to think about it). Went back to the board and shorted out Earth to red phase neutral bar and white phase neutral bar and both RCD'S tripped.
This just shows that you can't be to reliant on testers , as my rcd tester was still causing a trip.


when you did external fault loop impedance test, that would pick up a dodgy earth connection.
 

Reply to RCD Question in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
341
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
563
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
789
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
764
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock