Hi guys,
Just a quick query here. I have just gone into a property and done a EICR. Its a rewireable fuseboard with no rcd protection on any circuits. The main house ring circuit has an occurence with a spur off a spur. Easy to rectify i know but as i am going to to re-feeding the sockets, is there any requirement for me to protect the circuit with an RCD?

Many thanks in anticipation,
Dave
 
Hi guys,
Just a quick query here. I have just gone into a property and done a EICR. Its a rewireable fuseboard with no rcd protection on any circuits. The main house ring circuit has an occurence with a spur off a spur. Easy to rectify i know but as i am going to to re-feeding the sockets, is there any requirement for me to protect the circuit with an RCD?

Many thanks in anticipation,
Dave
Just from what you have said, C2 for no RCD for socket outlets, C2 for multiple spurs - overload risk, C3 for No RCD for cables concealed <50mm in walls. Quote for new CU and rectify ring spurs. Nice little remedial for you.
 
Just from what you have said, C2 for no RCD for socket outlets, C2 for multiple spurs - overload risk, C3 for No RCD for cables concealed <50mm in walls. Quote for new CU and rectify ring spurs. Nice little remedial for you.

why is a new CU required?

he is merely asking if any work he carries out needs RCD/RCBO protection.

Oh and sockets without RCD/RCBO protection is a C3, if it complied when installed, unless they can be used outdoors.
 
why is a new CU required?

he is merely asking if any work he carries out needs RCD/RCBO protection.

Oh and sockets without RCD/RCBO protection is a C3, if it complied when installed, unless they can be used outdoors.

Just from what you have said, C2 for no RCD for socket outlets, C2 for multiple spurs - overload risk, C3 for No RCD for cables concealed <50mm in walls. Quote for new CU and rectify ring spurs. Nice little remedial for you.

Rephrase that to “nice little earner for you.
 
It seems to be meggermans standard response to every post about doing a job in a house without RCD protection.

Ok, in complete contrast to your make do and mend philosophy, which then will get done by someone else later and they can pay again. Also as Inspector it is my discretion what I code non-compliances. Maybe you worth noting it would be reasonable to expect that any downstairs socket outlet could be used to supply equipment outside.
 
Ok, in complete contrast to your make do and mend philosophy, which then will get done by someone else later and they can pay again. Also as Inspector it is my discretion what I code non-compliances. Maybe you worth noting it would be reasonable to expect that any downstairs socket outlet could be used to supply equipment outside.

Make do and mend yes, they are asking to repair a small part of the installation not change i all completely, besides installing a new DB could lead to a whole load of problems which would cost the customer even more money that they didn't need to spend.

Yes the coding is down the inspector, as I said no question was asked about coding.

Again I pointed out if the sockets could be used outdoors, please read the whole reply before replying as it just makes you look ignorant and choosing what you want too read.
 
Make do and mend yes, they are asking to repair a small part of the installation not change i all completely, besides installing a new DB could lead to a whole load of problems which would cost the customer even more money that they didn't need to spend.

Yes the coding is down the inspector, as I said no question was asked about coding.

Again I pointed out if the sockets could be used outdoors, please read the whole reply before replying as it just makes you look ignorant and choosing what you want too read.[/QUOTE

I did read you post. Oh and sockets without RCD/RCBO protection is a C3, if it complied when installed, unless they can be used outdoors. . I am saying they can all be used outdoors.
Also, the guy has just carried out an EICR, this is the best time to now carry out DB replacement as he has inspected and tested installation so knows what faults are present. Why would that lead to problems?
 

Reply to RCD required? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
354
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
212
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
699
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock