Discuss RCD TEST Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

mark22

Help Please

I have installed a new supply to a garage. It is fed from a split board consumer unit in the house and is protected by an 80amp RCD.

I have installed a consumer unit in the garage which has a 40 amp RCD. (cu earthed via earth rod).

I carried out an RCD test and got the following results :

x1 27ms at 0 tripped garage
17ms at 180 tripped garage
x5 4ms at 0 tripped garage
7ms at 180 tripped house

My question is why does it only trip in the house on x5 at 180 and is the only way to resolve this by removing the circuit away from the rcd on the main board.
thanks
Mark
 
Its a combination of what each RCD is seeing at the time of your test. As the house will see a different load to the garage your results are really meaningless. If you try and test 2 RCDs in series like that it will only end up one way, - disappointing. Might be worth starting again with the design. cheers P&S
 
Help Please

I have installed a new supply to a garage. It is fed from a split board consumer unit in the house and is protected by an 80amp RCD.

I have installed a consumer unit in the garage which has a 40 amp RCD. (cu earthed via earth rod).

I carried out an RCD test and got the following results :

x1 27ms at 0 tripped garage
17ms at 180 tripped garage
x5 4ms at 0 tripped garage
7ms at 180 tripped house

My question is why does it only trip in the house on x5 at 180 and is the only way to resolve this by removing the circuit away from the rcd on the main board.
thanks
Mark

you have the answer in the last part of the post.
 
Is the house also TT
and if the house trips on X5 only why is there a problem you still need to protect the cable to your new Unit
 
Last edited by a moderator:
Mark,

A couple opossessions...

1. Is the garage down the garden from the house or connected to it?
2. What earthing arrangement do you have at the house? TT, TN-S, TN-C-S
3. Is the RCD in the main board a time delay RCD or just normal?
4. This earth rod, is it a screwdriver jabbed in the ground or a proper rod, details please, size etc...
5. On the basis you used SWA to feed to sub board, did you ground the steel wire and if so, which end?

Do you have any knowledge or understanding of sine waves or how RCD's work? I am going to guess and say no.
 
Here we go yet again!! The dreaded garage ''I can't 'export PME'' and the ''tripping of series connected RCD's'' !! When will they ever learn??

No-one ever seems to search on here for similar threads, it would save these OP's a lot of time and, ....stay well under cover of the barrage of well deserved abuse!! lol!!
 

Reply to RCD TEST Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
933
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
907
Hi My main feed comes into the garage, feeds into the meter and then out to another box with a 60AMP fuse then into the house...
Replies
20
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
529

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock